Different overnight discharge between batteries - oddly a difference battery each time...

Glenpk

New Member
Joined
Aug 8, 2022
Messages
8
Hi All,

I have been a reader on this forum for about 2 years and taken the plunge in setting up my own system (with questionable success).

I am currently using a Growatt SPF 5000 es. I have 3x Delongtop 51.2v 200ah batters connected in paralell (no bus bar) and have 2 main challanges.

1) When connecting the RS485 and using Lith (L02) the charging seems to be capped at about 500w. On USE 2 it will run at 2500w+ This is basically what my solar panels are able to produce as I am running a single string of Jinko 440w x 7. I have a second string ready to install but working one thing at a time. (we are only running a fridge at the moment).

When I use the Lith setting I get very arcuate % reading (e.g 94% etc) so it appears to be communicate. USE2 on the other hand gives the 25% groups (e.g 50%,75%, 100% only).

Does anyone have any suggestions as to why my BMS might be capping the amps in and what I might do about it?

2) overnight there seems to be a fair amount of discharge. (estimate 5.0kw) the. I am getting uneven battery discharge . The odd thing is it is a different battery each night.

Night 1 - battery 1 (68%), battery 2 (74%) battery 3 (74%)
Night 2 - battery 1 (92%), battery 2 (74%) battery 3 (92%)
Night 3 - battery 1 (74%), battery 2 (97%) battery 3 (74%)
Night 4 - battery 1 (54%), battery 2 (90%) battery 3 (90%)

I understand that generally the discharge should be consistent. The batteries are all brand new (just installed in the last week).

Should I be concerned and if so what should I be doing?
 
Many BMS don't register small currents. They might not accurately record even 100W/battery, and if that varies a little, it could account for randomness.

Do you notice any batteries suddenly jumping to 100% rather than a steady climb up?
Hi Subshine

Not that I am aware of.

Apart from the cap when using the BMS protocol, the charging seems normal.

I have learned from the manufacturer that the batteries apparently use a Pace BMS.

Interestingly, yesterday all three batteries were at 84% in the morning. Perhaps a settling in period?
 
Hi Subshine

Not that I am aware of.

Apart from the cap when using the BMS protocol, the charging seems normal.

I have learned from the manufacturer that the batteries apparently use a Pace BMS.

Interestingly, yesterday all three batteries were at 84% in the morning. Perhaps a settling in period?

Could be. Some BMS also require a handful of cycles and charges to full to accurately compute SoC.

You can always use a clamp DC ammeter to directly measure the current each battery is flowing. If they're within 5-10% of each other, you should be good.
 
Could be. Some BMS also require a handful of cycles and charges to full to accurately compute SoC.

You can always use a clamp DC ammeter to directly measure the current each battery is flowing. If they're within 5-10% of each other, you should be good.
Thanks for the tip. Any thoughts on why the BMS might be limiting the charge?
 
1) When connecting the RS485 and using Lith (L02) the charging seems to be capped at about 500w. On USE 2 it will run at 2500w+ This is basically what my solar panels are able to produce as I am running a single string of Jinko 440w x 7. I have a second string ready to install but working one thing at a time. (we are only running a fridge at the moment).

When I use the Lith setting I get very arcuate % reading (e.g 94% etc) so it appears to be communicate.

The AiO is reporting the BMS-reported SoC.

USE2 on the other hand gives the 25% groups (e.g 50%,75%, 100% only).

In this mode, it's just guessing.

Does anyone have any suggestions as to why my BMS might be capping the amps in and what I might do about it?

When in closed loop mode, the batteries tell the AiO how much current it can send to the battery.

I would confirm you have the batteries properly configured. When connecting multiples, there are often specific DIP switch settings for each battery.
 
Could be. Some BMS also require a handful of cycles and charges to full to accurately compute SoC.

You can always use a clamp DC ammeter to directly measure the current each battery is flowing. If they're within 5-10% of each other, you should be good.
Thanks for the tip. Any thoughts on why the BMS might be limiting the charge
 
Looks like our issue is maintained Battery 3 is 68.11% Battery 2 81.78% and Batter 1 58.56% this morning :(.

The system is set up on our little farm so I will double check the DIP switch config this weekend, although I am relatively confident it is OFFF, FOFF & OOFF

I have found out from the manufacturer that the BMS installed is a 16s200a Pace. I have downloaded that believe is the PC software.
 