robbob2112
Doing more research, mosty harmless
Between the battery and the inverter/charger the current flows both ways so you cant use a polarized breaker... fixed it
He removed the video because some people complainedView attachment 284164
From web page here:
![]()
DHM1X-2P Molded Case Circuit Breaker
www.nsbjd.com
I will say this appears to be a rebadging company, and this looks curiously the same as the TAIXI breakers that are in the breaker box Will recently panned, as they didn't perform to spec.
edit: now I can't find where he tested the breakers....edit 2 Nada...I must have dreamed it...I was left with the impression I couldn't rely on these breakers beyond on/off, they wouldn't protect the wires?
They're the same width as the DHM1X but longer and taller.OK that's pretty cool.
Now I wish I had those instead of the DHM1X. Just because that could be useful in a way.
Dang it.
If I hit the "OH $#!!" button (the RSD on the exterior of the house for example) the inverter could not only shut itself down but every battery right at the source.They're the same width as the DHM1X but longer and taller.
Just curious, what would you use the shunt trip for on a residential job?
I have one of these with the shunt trip sitting in a bin waiting to be used for that exact purpose.If I hit the "OH $#!!" button (the RSD on the exterior of the house for example) the inverter could not only shut itself down but every battery right at the source.
My ultimate goal is to have every battery breaker able to be shunt tripped.OK that's pretty cool.
Now I wish I had those instead of the DHM1X. Just because that could be useful in a way.
Dang it.
True, but then why is it marked with line and load sides? Something is a bit odd there.On the polarity issue from the previous pages: When using both poles with a battery, current flow is opposite in the two poles. It makes no difference whether in at top or out at top. The arc happens at the contacts and in the arc chute either way.
It's just convention:Yep, saw that in the instruction sheet too. But then....why line and load sides? Some reason other than polarization? Not knowing for sure I'm opting for the DHM3Z.
Is there any full size breaker of that capacity rating that is polarized? Generally I've seen them with the smaller mnepv midnite breakers, with the non polarized versions lacking the ++ and -- markings.I'm sure you're probably right about the DHM1X being nonpolarized. But there can be more to it than convention. If this was a listed breaker and wasn't marked line and load, you would know it was non polarized because the UL White Book requires it to be. It could be marked and still be nonpolarized as apparently some of the midnites are.
As was said in the thread you linked, I would believe Midnite's claims about a listed breaker. But who knows with an unlisted Chinese product? For me theres already a degree of uncertainly around using it at all. I just feel better about using the black ones.![]()
True, but then why is it marked with line and load sides? Something is a bit odd there.
Dihool makes the DHM3Z specifically for the battery to inverter circuit and it has a higher interrupt rating than the DHM1X. And being black it will show less dirt than the white one.![]()