timselectric
If I can do it, you can do it.
- Joined
- Feb 5, 2022
- Messages
- 18,551
I agree.
That's why I said maybe 2.
Doubtful it could be more than that.
That's why I said maybe 2.
Doubtful it could be more than that.
I definitely have to check up on this. i would assume (Would ofcourse checked first) that they work like normal batteries. Maybe the problem lies in the bms?Yes, in parallel.
Yes ill have to check up on this.You would have to check the battery specs to see how many you can put in series. Could only be rated for 2 in series. They are usually used in parallel for 48v systems.
Thanks for your timeI agree.
That's why I said maybe 2.
Doubtful it could be more than that.
How else do i get a good 20-30 kwh system that is not to expensive and that i can do 10-15kw draws?
Yes ill have to check up on this.
How else do i get a good 20-30 kwh system that is not to expensive and that i can do 10-15kw draws?
As some said above, the batteries are not the problem, it's daisy chaining the BMS that's not such a good idea and I don't think they will recommend building a high voltage battery with their units due to people killing themselvesWhy would you not? I see them in server racks on youtube quite often
As some said above, the batteries are not the problem, it's daisy chaining the BMS that's not such a good idea and I don't think they will recommend building a high voltage battery with their units due to people killing themselves
But theoretically, it should work, and the units should also remain within spec. The voltages over each unit remain the same. And the amps running through each BMS usually remains the same as well. The growatt you listed can only draw 25A anyway:
Excellent point. Indeed, I didn't account for breakdown voltages. But you could then just as well replace the FET's on the BMS with beafier rated ones up to 400V (edit: actually I'm wrong here after some thinking, the entire PCB needs to be customized for HV) ?To make this work, I think all disconnects would have to switch together. For instance, a 4PST relay, each contact able to handle the 60V or so open-circuit of the battery. Coil would have to be driven by a signal that is the "AND" of the connect signal from each battery, e.g. four relays in series.
Btw, from the above datasheet it's clear that Growatt is using per 'module' 16 LifePO4 cells of 50Ah in series.DATASHEET ABOVE
96x50AH | 15,36 kWh | € 3 673,68 | € 0,24 / Wh |
96x100AH | 30,72 kWh | € 5 005,68 | € 0,16 / Wh |