I’ve been considering the issue where even short surge amounts of grid backfeed are causing people to get a knock on the door from the PoCo. We all know “zero-export” inverters do not limit backfeed power to zero, but they try. For those of you who don’t believe this, please search the forum.
I’ve looked for devices that will actively monitor the current direction and take an action when reverse current flow is indicated. The only thing I’m finding are “Reverse Power Relays” meant to prevent generators from motoring. I’ve even seen schematics for these, and they are all cheap low-performance analog circuits. I believe a modern digital approach could yield a high-performance solution.
It should be easily possible to sample voltage and current simultaneously using a CT, and calculate both power factor and current flow direction on a per-cycle basis. Sampling rate should be like 240 Hz (or 200 Hz for 50Hz countries) to capture the zero crossings cleanly. I’m aware that CTs have a time constant, and that averaging over multiple cycles will be necessary to minimize noise. Some calibration will likely be necessary. For the sake of argument, let’s say this is all feasible, and I’ve constructed such a detector in a microprocessor with thresholds for power and duration of reverse transient.
What action should be taken when the reverse current flow detector activates?
• Disconnect the mains via a contactor or relay?
Where will the excess power go, back into the battery (hopefully)?
• Switch in a resistive load (could be as high as 5 kW) for the second or two to absorb the power before it goes to the grid?
This would need thermal and timeout monitoring for safety, and would be as big as those huge resistive loads Will was using.
• Any other ideas?
I’ve looked for devices that will actively monitor the current direction and take an action when reverse current flow is indicated. The only thing I’m finding are “Reverse Power Relays” meant to prevent generators from motoring. I’ve even seen schematics for these, and they are all cheap low-performance analog circuits. I believe a modern digital approach could yield a high-performance solution.
It should be easily possible to sample voltage and current simultaneously using a CT, and calculate both power factor and current flow direction on a per-cycle basis. Sampling rate should be like 240 Hz (or 200 Hz for 50Hz countries) to capture the zero crossings cleanly. I’m aware that CTs have a time constant, and that averaging over multiple cycles will be necessary to minimize noise. Some calibration will likely be necessary. For the sake of argument, let’s say this is all feasible, and I’ve constructed such a detector in a microprocessor with thresholds for power and duration of reverse transient.
What action should be taken when the reverse current flow detector activates?
• Disconnect the mains via a contactor or relay?
Where will the excess power go, back into the battery (hopefully)?
• Switch in a resistive load (could be as high as 5 kW) for the second or two to absorb the power before it goes to the grid?
This would need thermal and timeout monitoring for safety, and would be as big as those huge resistive loads Will was using.
• Any other ideas?