Well, more like a real indicator of grade B cells. Matched cells will stay within a single digit millivolt difference (I have grade B and matched grade A to compare). Generally speaking, mine stay within 4 to 8 millivolts apart through 99.9% of the charge/discharge cycle for the grade A (depends on the C rate, and also the connections). Grade B cells are a good value.
Well, as long as my cells are in between the knees (roughly between 3.1 - 3.4v) the highest I've seen was a delta of 10mv. Most of the time less than 5. So the top balanced worked fine I would say.
Docan offered me a warranty extension and I took it. I'm pretty sure that the shipping costs for a replacement cell would be more less the same as the cost for a new cell. But I appreciate the gesture.
Anyhow, some new issue arose (like always):
I set the following parameters for solar cycling:
Bulk charge: 27.2
Float (the SCC manual calls it recovery charge but it behaves exactly as float): 26.8
Float is meant to serve loads when battery is full. This works nicely. When I pull bigger loads while in float the panels are mostly able to serve.
However, one charger (I have 2 because of different panels) never reaches bulk. It's having a south orientation and therefore sees sun roughly 2 hours after the east panels. Once it does, the battery voltage is already over 26.8v and the charger interprets that as fully charged and therefore drops to float while the other controller is still in bulk.
Anyone having a good idea about this situation?