Hi all, new recruit to the Solar Forum here!
I'm in the process of setting up an Ecoworthy 5000W/48V All-In-One (apparently an SRNE-HF rebadge) with Pytes V5' server rack batteries.
Having read the supplied manuals, then downloaded manuals for several different similar models to piece together the missing information (undocumented settings!) ... I wanted to post what I found worked for this combination, and to sanity check that this is correct.
At the Ecoworthy AIO:
Parameter 32: Changed default SLA to BMS to allow the BMS to control charging current, and enable hidden BMS related settings
Parameter 33: BMS Protocol, change default WoW to PAC (PACE) as this is the dual-BMS used in the Pytes V5'
Parameters 39, 58-62: These new parameters appear for setting SOC based maximum/minimum points as per the SRNE-HYP series manual.
At the Pytes V5':
Set the undocumented "ADD" DIP switches to 101000 (that's 1 and 3 ON) for "SRNE" protocol mode to match the inverter's original type.
Finally: The comms cable ...
The Ecoworthy uses an RS485 link. It provides +5v/0v on pins 1/2 respectively, and RS485A/B on pins 7/8.
The Pytes RS485 port allows for RS485 on pins 1/2 OR 7/8 -- note these appear to be shorted together internally (1 to 8, 2 to 7) from continuity testing.
Therefore: Using a regular all-wired network patch lead here would send 5V from the inverter (1,2), to the battery (1,2), and then back up (7,8) to the inverter. I don't want to do that, right?
I have cobbled together a junk CAT-5 lead adapter which connects ONLY pins 7-7 and 8-8, ignoring possible CAN bus pins (4,5) and grounds (3,6).
This allows the two to communicate.
Q: Is it acceptable to leave it at that, and make a custom lead with just those two conductors, no GND, no screen?
When it is working: You gain an extra (undocumented) page on the settings, right after standard page 1 "Input Battery/Output AC" voltages.
You get page 1a: "Battery Voltage according to BMS" and "State of charge%"
When it's not working: If BMS is enabled [in 32] then a wrong protocol/DIP address/wiring gets you an "Error 58" on the display of the Ecoworthy, and the "LI" icon flashes to complain about battery comms. If [32] is set at SLA still, I don't think you get any feedback on whether you're right, wrong, or otherwise! At least it felt like that until I blundered into that option.
I hope this helps someone looking for info on one or both of these items.
Mike.
I'm in the process of setting up an Ecoworthy 5000W/48V All-In-One (apparently an SRNE-HF rebadge) with Pytes V5' server rack batteries.
Having read the supplied manuals, then downloaded manuals for several different similar models to piece together the missing information (undocumented settings!) ... I wanted to post what I found worked for this combination, and to sanity check that this is correct.
At the Ecoworthy AIO:
Parameter 32: Changed default SLA to BMS to allow the BMS to control charging current, and enable hidden BMS related settings
Parameter 33: BMS Protocol, change default WoW to PAC (PACE) as this is the dual-BMS used in the Pytes V5'
Parameters 39, 58-62: These new parameters appear for setting SOC based maximum/minimum points as per the SRNE-HYP series manual.
At the Pytes V5':
Set the undocumented "ADD" DIP switches to 101000 (that's 1 and 3 ON) for "SRNE" protocol mode to match the inverter's original type.
Finally: The comms cable ...
The Ecoworthy uses an RS485 link. It provides +5v/0v on pins 1/2 respectively, and RS485A/B on pins 7/8.
The Pytes RS485 port allows for RS485 on pins 1/2 OR 7/8 -- note these appear to be shorted together internally (1 to 8, 2 to 7) from continuity testing.
Therefore: Using a regular all-wired network patch lead here would send 5V from the inverter (1,2), to the battery (1,2), and then back up (7,8) to the inverter. I don't want to do that, right?
I have cobbled together a junk CAT-5 lead adapter which connects ONLY pins 7-7 and 8-8, ignoring possible CAN bus pins (4,5) and grounds (3,6).
This allows the two to communicate.
Q: Is it acceptable to leave it at that, and make a custom lead with just those two conductors, no GND, no screen?
When it is working: You gain an extra (undocumented) page on the settings, right after standard page 1 "Input Battery/Output AC" voltages.
You get page 1a: "Battery Voltage according to BMS" and "State of charge%"
When it's not working: If BMS is enabled [in 32] then a wrong protocol/DIP address/wiring gets you an "Error 58" on the display of the Ecoworthy, and the "LI" icon flashes to complain about battery comms. If [32] is set at SLA still, I don't think you get any feedback on whether you're right, wrong, or otherwise! At least it felt like that until I blundered into that option.
I hope this helps someone looking for info on one or both of these items.
Mike.