marionw
Solar Wizard
A Double breaker in the main panel which would feed both inverters. The double breaker outputs L1 and L2 (240vac). L1 and Neutral gets wired to inverter 1 and L2 and Neutral gets wired to inverter 2.Thank you. Who knows, maybe the Cat 5 cable will show different info. But i doubt it.
In the picture I have or thought the "right" inverter was the master and the one on the "left" was the slave.
The right inverter is set to ID1 & 2P0, the left inverter is set to ID2 & 2P2. I would have thought the right would be the master. Tell me if i should switch the settings on them or not please.
The right inverter has grid input hardwired to it via means of a single pole 40 amp breaker in the main panel. It's providing 120V.
The left inverter you see that has a 10 gauge extension cord hard wired to it was for testing purposes only and I plugged it into a 15 amp outlet to charge the batteries. ( I'm considering this a back up mean of charging - this means of charging is limited because it's only a 15 amp breaker that i would plug into.
I don't think the battery is got down to 20% SOC, the inverters are still reading 52.4 volts. Connecting the app to the batteries is difficult for me but I managed to get one to connect and it still said 40% state of charge.
Still confused on which one is the master and which one is the slave..
I don't think anything I have is able to switch back to the grid because I have a manual sub panel transfer switch. It has "line" "off" and "gen". So if I have the transfer switch in gen, which I did for the overnight test, does not have the ability to switch itself back to grid via my sub panel.
Where you mention this,
In PV1ST or BT1ST, when you turn the power on/off rocker switch to off and with grid input the inverter will go into standby (shows as an icon on the lower right of the inverter screen). The AC Out/Load will turn off. The screen will time out and go blank but touching any of the controls will wake the screen back up. I never turn this switch to off before leaving it for the overnight test. It was still in the on position upon waking up and They're inverter Did not respond to me pressing any of the buttons so I had to toggle it off and then back on. This was on the right inverter.
For the dip switches I have the top one set as one and I thought that was the master battery in the one that has the dip switch in two was the slave.
Based on what you said about the positive and negative wires from the battery to the inverters. This is how I have them now, but rereading your response it seems that I need to have the negative cable connected to where my finger is pointing, yes?
I'm confused about the last paragraph mentioning 240 going to the inverters. Would you suggesting that I'm supposed to have a 2 pole 40 amp breaker instead of the single 40 amp breaker?
You can see what the right and left inverters are set to in the photos.
Eco worthy email customer service is not helping much, this is 100x more informative, so thank you
L1 and Neutral = 120vac, L2 and Neutral = 120vac. Each inverter can only take 120vac on it's grid input. Leaver the breakers on the left side of the inverter off until you measure the voltage on the AC/Grid terminals in the inverter to ensure you only have 120vac on these terminals.
The breaker on the left side on the Inverter needs to be on only if you want grid power into the inverter. It can be off if you want but the inverter would never be able to automatically shift to grid (bypass) if PV Array and battery cannot support the loads. This would be similar to an entirely off grid setup where there is no "grid" available. You could turn them on and shift the inverter to AC1ST if you need to charge the batteries.
If as you implied the "Main" panel did not have grid input as the input was from the Transfer switch then event the hard wired inverter did not have grid input
You can have either inverter as Master, doesn't matter.
The right inverter could not go into standby as there was no grid input. If the battery and PV array are not enough to support the load output the inverter will shut down because with no grid input it can't shift into bypass. It's possible some load on the subpanel kicked on (hot water heater?) that caused the inverter to shut down.
For the negative cable yes, connect to the bottom battery. This is a normal connection for multiple batteries connected in parallel to better force all batteries to equally support the load.
You might find that additional batteries would be a good thing to add as your budget allows.