So far in my testing this appears to be a solid AIO. The ECO-Worthy 5KW does have a Menu Item 34.
I may have to buy a second just to evaluate the parallel/240vac performance.
I will test whether this AIO feeds (or can feed) back to the grid.
I have "Grid/Utility" input from a 120vac outlet. I have a switch installed in the extension cord inline with the black/hot as I wanted to evaluate the Neutral and Ground bond in the Inverter, particularly between Grid In and AC out. Menu Item 63 (N-G Automatically Connect) is poorly worded in the user manual (on or off, no automation), if Enabled a relay bonds the AC out Neutral and Ground. If Disabled the relay is deenergized and there is no bond. I need to further verify if because the AC In neutral and ground are bonded back at the main panel, by bonding the AC Out does it also bond the AC In via the AC out ground bond.
I have mapped all the "Menu Items" to their respective Modbus registers and have verified them.
This is my test setup sitting right next to my computer.
I can modify any menu setting from this screen which also means I can automate it
Monitoring