EG4 Support set them to that. I have one EG4 LL-s 48v and a Vatrer 48v 100 ah battery.why is your discharge limit set so low. That’s only going to give you 5000w max. What batteries do you have?
You need more battery. You should probably set to 200 since you have two batteries. What is the max discharge rate of each? If each battery is limited to 50a max discharge you need to keep it at 100a. I would just get at least two more batteries.EG4 Support set them to that. I have one EG4 LL-s 48v and a Vatrer 48v 100 ah battery.
3 ton heat pump. Lights ect. Never showed a reading over 4k but maybe a spike on start up.yes, possibly. What were you powering?
If you don't have one you might consider putting a soft start on your a/c. I have a 3 ton that a soft start reduced the in rush current from 81 amps to 29.3 ton heat pump. Lights ect. Never showed a reading over 4k but maybe a spike on start up.
I amAre you running the latest firmware?
How can I check what in rush I am experiencing ?If you don't have one you might consider putting a soft start on your a/c. I have a 3 ton that a soft start reduced the in rush current from 81 amps to 29.
It would appear you're in closed loop mode which because you have two different brands of battery the inverter is probably only communicating with the single LL s 100 ahr battery. The only option is to switch to voltage mode and manually set the Ahr value to 200. This should allow you to set the discharge amperage to 200.
Well it does in fact run it heating at night and cooling in the day.I don’t see any way 100amp of battery is going to start a 3ton heat pump without softstart.
AvgJoe just did a video with two Vater batteries starting a 3ton with a softstart and batteries were config’d for full 100amp each.
Any suggestions for a soft start for a 3 ton ?If you don't have one you might consider putting a soft start on your a/c. I have a 3 ton that a soft start reduced the in rush current from 81 amps to 29.
The two most prevalent brands are the $375 EasyStart or the $250 Hyper Engineering. The EasyStart has bluetooth does provide some info. I went with the HyperEngineering cause it does the same thing without the IMO bells and whistles. Also the Hyper was smaller which fit under the A/C's cover keeping it completely out of sight and the sun.Any suggestions for a soft start for a 3 ton ?
Ok. I am looking at soft starts now. Seems to range from 160.00 to 450.00. That’s a big range lol.Your LRA or in rush is 75 amps. A soft start will drop that to less than 25. Highly recommended. Your inverter at max output (not surge) is 50 amps.
The link shoes 230v. I’m in the USThis is the one I'm using. My a/c's rla is 16.1 amps... yours 14.7
![]()
Sure-Start Products
Premier Components Supply offers electronic software-driven soft starters that are used for a dramatic reduction in start-up current for 1 phase AC compressors.premiercomponentssupply.com