Putting this out there for anyone interested in some holiday reading. Any and all feedback appreciated!
For those following along, you know I haven’t been much of a “make a plan and stick with it!” kind of DIY’er. I’ve been through several design and equipment iterations for a solid 3 years now. Problem is the more I learn, the more ambitious I get. It also doesn’t help that new hardware seems to be released just as I commit to something! See exhibit A —
Thread 'Dual EG4 6000XP Wiring'
https://diysolarforum.com/threads/dual-eg4-6000xp-wiring-please-review.78087/
The 6000’s were sold, 12000 received, and here we are. This time I made sure to get it installed and running in a temporary configuration before the next new thing is released
Design decision points:
Thanks and Happy Holidays!
For those following along, you know I haven’t been much of a “make a plan and stick with it!” kind of DIY’er. I’ve been through several design and equipment iterations for a solid 3 years now. Problem is the more I learn, the more ambitious I get. It also doesn’t help that new hardware seems to be released just as I commit to something! See exhibit A —
Thread 'Dual EG4 6000XP Wiring'
https://diysolarforum.com/threads/dual-eg4-6000xp-wiring-please-review.78087/
The 6000’s were sold, 12000 received, and here we are. This time I made sure to get it installed and running in a temporary configuration before the next new thing is released

Design decision points:
- This is in a remote cabin currently on grid. The objective is to be 100% self-sufficient but still use the grid for backup power when needed.
- N-G bond only at the 200A Service Main (figure 1).
- I need to be able to easily talk anyone through switching PV off completely. Using the 100A non-fused manual transfer switch to do that (figure 2) with 100A breakers feeding it from each side.
- All 100A runs are using 3AWG THHN wire.
- 6 AWG bare copper or THHN for all grounding.
- Dedicated PV sub-panel (figure 3.) for local (PV-only) loads and allow for isolation (this was previously the combiner panel for the 6000 XP’s).
- Single 12000 XP (figure 4), grid provides AC input for backup / bypass purposes only.
- 2 x EG4 280Ah Indoor batteries (figure 5). Paralleled and wired directly to inverter.
- IMO disconnect at each end of the PV cables (figure 6).
- 2 strings of 4 (4S2P) 455W Solarever panels (figure 7), plan to go to 8S2P. Ground array ~90ft from solar shed.
- House main sub-panel for all loads (figure 8). This is currently the main, but will become a sub-panel when the service main panel is installed.
Thanks and Happy Holidays!