We currently have a 3.78kw solar system installed in 2019- with Delta grid-tied inverter and 20A backfed breaker on the main panel. I'm planning to remove this inverter, and upgrade to an EG4 12kPV, and in the future add battery and more PV panels.
Our home has a 200A main panel (pics attached). There is no main breaker on the panel, but there is a group of 125A sub-feed lugs which I don't really understand.
Thinking about the NEC 120% rule, the EG4 12kpv has max output 33.3A. 33.3Ax125% is 41.6A, so I think we're supposed to replace that 20A solar breaker with 45A, but that would exceed 120% of a 200A panel. So I guess we'd need to derate the panel? Or are those sub feed lugs already derating the panel to 125A? OR- should I simply use a 40A solar breaker and call it a day?



Our home has a 200A main panel (pics attached). There is no main breaker on the panel, but there is a group of 125A sub-feed lugs which I don't really understand.
Thinking about the NEC 120% rule, the EG4 12kpv has max output 33.3A. 33.3Ax125% is 41.6A, so I think we're supposed to replace that 20A solar breaker with 45A, but that would exceed 120% of a 200A panel. So I guess we'd need to derate the panel? Or are those sub feed lugs already derating the panel to 125A? OR- should I simply use a 40A solar breaker and call it a day?