Hi all. I'm new here, and I'm in the final stages of my off grid, 4,000 square foot barndominium build in southern coastal Texas. If this post is in the wrong place, I apologize and feel free to move it. When I first installed the 18k and battery banks, everything seemed fine. I could even run a heat gun on low (did it to soften some plastic for plumbing purposes). Then the firmware updates started happening... and things kept getting worse and worse. As it stands now, I'm not sure I'll be able to live in there without solving some of these issues.
First, the (current) setup:
- EG4 18k inverter
- 12x EG4 LL batteries
- 5 NE solar panels (just to keep the batteries charged while under construction)
- Ultimately, will have 24 panels in 2 strings
- 4 EG4 solar mini splits - 2x 2 ton units, 2x 1 ton units. 1 2 ton and 1 1 ton run off of 7 and 5 panels respectively
- Chargeverter and 6kW inverter backup charging generator
Now, on to the problems.
- I'm very sensitive to flicker. So all the bulbs/fixtures in the living space are Philips Eye Comfort/flicker free fixtures. Up until the last firmware update (1E1E, iirc), there didn't seem to be any led flicker. Now it looks like this - the camera is giving an accurate representation of what the flicker looks like:
- About a month ago, I dragged out an older (read: non-computerized, but in excellent shape) washing machine the previous owner left in a barn on the property so I wouldn't have to go to the laundromat anymore during construction. It worked fine. Then, (going by memory as best as I can remember), after a firmware update (prior to the 1E1E update), I suddenly started getting faults (and loss of power), specifically "vbus out of range." Every ten minutes or so. With the latest firmware update, the faults are now virtually continuous. I have to run the washing machine with a generator now. Except with the new firmware, the faults are now referred to as, "E019: Bus voltage high"
- One of the batteries started cycling between "standby" and "discharge" when all the other batteries were showing discharge, I've since disconnected that battery in hopes that it would resolve the next issue. It hasn't.
- Constant battery discharge. Even with only 5 panels connected, I'm still getting significantly more PV input than load. So much so, that unless the inverter is idling at a huge draw, the batteries should be a 100% SOC. They're not.
The top chart shows PV in; the bottom chart discharge for the same period.
Any help would be hugely appreciated. I'm hopefully going to get the cert of occupancy in the next couple of weeks and would love to not have to try to live with these problems.
First, the (current) setup:
- EG4 18k inverter
- 12x EG4 LL batteries
- 5 NE solar panels (just to keep the batteries charged while under construction)
- Ultimately, will have 24 panels in 2 strings
- 4 EG4 solar mini splits - 2x 2 ton units, 2x 1 ton units. 1 2 ton and 1 1 ton run off of 7 and 5 panels respectively
- Chargeverter and 6kW inverter backup charging generator
Now, on to the problems.
- I'm very sensitive to flicker. So all the bulbs/fixtures in the living space are Philips Eye Comfort/flicker free fixtures. Up until the last firmware update (1E1E, iirc), there didn't seem to be any led flicker. Now it looks like this - the camera is giving an accurate representation of what the flicker looks like:
- About a month ago, I dragged out an older (read: non-computerized, but in excellent shape) washing machine the previous owner left in a barn on the property so I wouldn't have to go to the laundromat anymore during construction. It worked fine. Then, (going by memory as best as I can remember), after a firmware update (prior to the 1E1E update), I suddenly started getting faults (and loss of power), specifically "vbus out of range." Every ten minutes or so. With the latest firmware update, the faults are now virtually continuous. I have to run the washing machine with a generator now. Except with the new firmware, the faults are now referred to as, "E019: Bus voltage high"
- One of the batteries started cycling between "standby" and "discharge" when all the other batteries were showing discharge, I've since disconnected that battery in hopes that it would resolve the next issue. It hasn't.
- Constant battery discharge. Even with only 5 panels connected, I'm still getting significantly more PV input than load. So much so, that unless the inverter is idling at a huge draw, the batteries should be a 100% SOC. They're not.
The top chart shows PV in; the bottom chart discharge for the same period.
Any help would be hugely appreciated. I'm hopefully going to get the cert of occupancy in the next couple of weeks and would love to not have to try to live with these problems.