I have a newbie question about MPPT range. I am planning an off-grid solar power system using an EG4 18K. I was thinking of installing a 10-panel array of Blue Sun Bi-Facial panels, model BSM460M-72HBD. The ground mount array will be approximately 100 yards from the inverter, so I am looking to maximize voltage to minimize voltage drop over that distance. The Voc of that array in series would be 502V under SOT, and 582V at -40C (what I am using as the theoretical max) based on the listed temp coefficient Voc.
While the EG4 18K is capable of taking 600V from a PV array, its MPPT range tops out at 500V.
I honestly don’t know how much that matters. Should I rethink my array to get the max Voc below 500V? In order to do that while keeping my voltage as high as possible it seems like I would actually have to increase the size of my array to 2 strings of 8 panels each, so 16 panels total. This would get the max voltage per string in the 400-500 range, depending on temperature, but would also mean more expense in panels, racking, etc. On the other hand, I also know that many people eventually upsize their array anyway...
I would appreciate thoughts from the very knowledgeable members of this forum. Thanks in advance!
While the EG4 18K is capable of taking 600V from a PV array, its MPPT range tops out at 500V.
I honestly don’t know how much that matters. Should I rethink my array to get the max Voc below 500V? In order to do that while keeping my voltage as high as possible it seems like I would actually have to increase the size of my array to 2 strings of 8 panels each, so 16 panels total. This would get the max voltage per string in the 400-500 range, depending on temperature, but would also mean more expense in panels, racking, etc. On the other hand, I also know that many people eventually upsize their array anyway...
I would appreciate thoughts from the very knowledgeable members of this forum. Thanks in advance!