zanydroid
Solar Wizard
The manual transfer switch hard bypasses the 18kpv if it shits a brick. So your house can have power even if the 18kpv brain completely dies or the whole box melts in a fireHi I’m new and apologize if this is a dumb question. If you connect the utility and meter to the grid port on the kpv 18, and then connect the load port on the kpv 18 to the main service panel, doesn’t this solve the issues you bring up? If the grid goes down, the ATS on the “input lugs” (I’m assuming that’s the grid port) will shut down the kpv 18’s output from the grid port. So no back feeding the grid. However your PV system and batteries will still be able to provide power to the main service panel through the load port on the kpv. Isn’t that basically what they do in this diagram? I just don’t understand the need for a supply side tap or manual transfer switch.
The supply side tap could well be pointless or counterproductive IE requires more labor or POCO approval, or is straight up un implementable if what you have is a combo meter main. You need to pick or design a wiring diagram based on your needs.