So I upgraded to 3 x EG4 18k for my whole house (mostly) off-grid system.
And now I have some problems to solve that I can't wrap my head around.
We've been 100% off grid solar for 2 years.
I wanted to add grid-backup (not sell-back) to my setup, so my generator would run less during the winter (noise, propane use, etc)
Here is what I had previously and what it could do (my old system):
Equipment list:
6 x Growatt 5000 = 30 kw inverter power (in parallel) and autotransformers x 2
124 kwh lifepower4 battery bank (24 batteries total)
NO grid
20kw propane Cummins backup generator (max about 18kw possbilbe)
36kw Solar (96 panels)
Additional 3 Growatt 5000 inverters taking just my generator input.
Victron Shunt to start and stop my generator (the Growatts couldn't do it)
Solar Assistant for monitoring
Setup:
My 6 Growatt inverters are connected to
(1) House - to supply up to 30KW A/C power (worked well)
(2) Battery bank
(3) Solar
Their only job was to supply the house at all times (day and night using solar plus/minus battery bank) and keep the battery bank topped off for nigh use/bad weather use.
My additional 3 Growatt inverters:
- Only connected to Generator and battery bank (the generator 240V output would be used to charge the battery bank) and was hooked up into grid input on the inverters. So it inverts the 240V input from the generator and acts just as a battery charger.
- Only one way from Genertor to Battery.
- no solar, no house connections.
- These 3 (total 15kw capacity) have only one purpose: charge the batteries when SOC < 15%
- Fired by the Victron shunt which reads the BMS of my batteries and turns on/off the generator.
This system worked well. Extremely well.
So, why change it?
Some limitations:
- no grid backup (and I want to use my generator less)
- Some growatts were breaking and I had to replace a few over the 2 years
- EG4 18K better/newer tech supposedly and can do it ALL??
- upgrade program to get to the EG4 18Ks.
- Growatts not able to directly manage generator, but had to rely on Victron shunt to do this.
- 9 x 70W per hour power consumption for all the Growatts = 630 W per hour just to keep them going. That's 15kw per 24 hours just to have the 9 inverters on the wall.
So, I took down all the 9 Growatts and replaced them with 3 x EG4 18k.
New setup:
- 3 x EG4 18k
- Same battery bank 124kwh
- Same solar panels (new arrangement in how they get to the inverters)
- Same generator.
- Grid backup (10kw limit due to transformer on my property)
The new setup is really nice looking and simpler all into each of the 3 inverters now:
- Generator wired to Gen input
- Grid wired to Grid input
- Solar input
- Battery bank
Order of operation should be simple and what I'm looking for: (but I can't get it to work like this):
(1) Use solar to charge batteries and power load (works)
(2) In absence of solar, use batteries to power loads (works)
What should work, but does NOT:
(3) When SOC of battery drops below 20%, use backup grid (10kw) to charge battery/help with load
(4) When grid not available use GEN instead (18kw) to charge battery/help with load
This works if the total Load is less than 10kw.
As soon as load exceeds 10KW (max of grid), my breakers flip on the grid side. The inverters try to draw more than 10K from grid.
It's like the inverter tries to get the whole load from grid.
What I would expect:
Load is 15kw. Inverter draws 10kw from grid and 5 kw from battery bank.
Load is 9kw. Inverter draws 10 kw from grid and supplies 1 kw to charge bank
Load is 4kw. Inverter draws 10 kw from grid and supplies 6 kw to charge bank.
Load is 25kw. Inverter draws 10 kw from grid and supplies zero to charge bank, draws the shortfall of 15kw from bank.
Under Application Settings, I have the max AC Input Power KW set to 3 (each inverter) so below the 10kw max I could draw. But it draws more than this limit.
I would expect this number to be the grand TOTAL that my inverter could ever draw from grid all inclusive.
I have AC charge enabled. and AC charge power is also set to 3 KW. So max battery charging should be limited to 9 kw for the total of 3 inverters.
Interestingly, below 10 kw total load, the inverters behave as expected. Meaning that if the load is 8 kw, then only 1 kw is used to charge batteries. If load is 3kw, then 6 kw is used to charge batteries. BUT as soon as load is 12k, then the inverters try to draw all of it from grid and none from battery bank. Not sure what to do.
So tech support suggested that the AC charge power for AC charge of battery bank is in ADDITION to the max AC Input Power KW set under the Application settings.
They suggested that I need to upgrade my grid to 25kw. But I will have the same problem as soon as my load goes to 26kw. It'll overload my grid and flip grid breaker. I would assume the same would also happen if grid was off and gen used instead. I'd hit a had top of maybe 18Kw for my generator. The answer here cannot be to get a 36kw grid connection and 36kw generator to match my max inverter output of 36kw.
Any help would be appreciated.
One solution I see is buying a 4th 18k inverter that just handles my grid and generator connection like my previous 3 Growatt inverters did.
So essentially:
Keep my 3 x 18kw EG4 and only connect them to Solar, battery and house.
They just supply the load, charge/discharge the bank using solar.
A 4th EG4 18k is ONLY there for handling my grid and generator inputs. It's only connected to Grid, gen and battery bank.
It does not communicated with the house, solar or the other inverters. (like my old setup above).
It reads SOC of battery bank. If SOC drops, it turns on grid just to "charge my battery" in the background. or fires Gen if grid is down to do the same.
The other 3 EG4s are none the wiser. They don't know anything and keep supplying the house with power no matter what, up to 36kw.
This setup worked well for me in the past. I'm tempted to repeat it, but with 4 x EG4 18k instead of 9 Growatt 5000 inverters.
Wow, long post.
I'm hoping there are just some settings I can tweak that will do this job for me with the existing 3 x EG4 18k that I already own instead of buying another one and adding it. But I will if there's no way around it.
In case you're curious why I would ever need that much load at all? Yes, I've loaded routinely in the teens and quite a bit in the 20s for charging my electric car, running all of our appliances and shop, etc.
Thanks,
Christian.
And now I have some problems to solve that I can't wrap my head around.
We've been 100% off grid solar for 2 years.
I wanted to add grid-backup (not sell-back) to my setup, so my generator would run less during the winter (noise, propane use, etc)
Here is what I had previously and what it could do (my old system):
Equipment list:
6 x Growatt 5000 = 30 kw inverter power (in parallel) and autotransformers x 2
124 kwh lifepower4 battery bank (24 batteries total)
NO grid
20kw propane Cummins backup generator (max about 18kw possbilbe)
36kw Solar (96 panels)
Additional 3 Growatt 5000 inverters taking just my generator input.
Victron Shunt to start and stop my generator (the Growatts couldn't do it)
Solar Assistant for monitoring
Setup:
My 6 Growatt inverters are connected to
(1) House - to supply up to 30KW A/C power (worked well)
(2) Battery bank
(3) Solar
Their only job was to supply the house at all times (day and night using solar plus/minus battery bank) and keep the battery bank topped off for nigh use/bad weather use.
My additional 3 Growatt inverters:
- Only connected to Generator and battery bank (the generator 240V output would be used to charge the battery bank) and was hooked up into grid input on the inverters. So it inverts the 240V input from the generator and acts just as a battery charger.
- Only one way from Genertor to Battery.
- no solar, no house connections.
- These 3 (total 15kw capacity) have only one purpose: charge the batteries when SOC < 15%
- Fired by the Victron shunt which reads the BMS of my batteries and turns on/off the generator.
This system worked well. Extremely well.
So, why change it?
Some limitations:
- no grid backup (and I want to use my generator less)
- Some growatts were breaking and I had to replace a few over the 2 years
- EG4 18K better/newer tech supposedly and can do it ALL??
- upgrade program to get to the EG4 18Ks.
- Growatts not able to directly manage generator, but had to rely on Victron shunt to do this.
- 9 x 70W per hour power consumption for all the Growatts = 630 W per hour just to keep them going. That's 15kw per 24 hours just to have the 9 inverters on the wall.
So, I took down all the 9 Growatts and replaced them with 3 x EG4 18k.
New setup:
- 3 x EG4 18k
- Same battery bank 124kwh
- Same solar panels (new arrangement in how they get to the inverters)
- Same generator.
- Grid backup (10kw limit due to transformer on my property)
The new setup is really nice looking and simpler all into each of the 3 inverters now:
- Generator wired to Gen input
- Grid wired to Grid input
- Solar input
- Battery bank
Order of operation should be simple and what I'm looking for: (but I can't get it to work like this):
(1) Use solar to charge batteries and power load (works)
(2) In absence of solar, use batteries to power loads (works)
What should work, but does NOT:
(3) When SOC of battery drops below 20%, use backup grid (10kw) to charge battery/help with load
(4) When grid not available use GEN instead (18kw) to charge battery/help with load
This works if the total Load is less than 10kw.
As soon as load exceeds 10KW (max of grid), my breakers flip on the grid side. The inverters try to draw more than 10K from grid.
It's like the inverter tries to get the whole load from grid.
What I would expect:
Load is 15kw. Inverter draws 10kw from grid and 5 kw from battery bank.
Load is 9kw. Inverter draws 10 kw from grid and supplies 1 kw to charge bank
Load is 4kw. Inverter draws 10 kw from grid and supplies 6 kw to charge bank.
Load is 25kw. Inverter draws 10 kw from grid and supplies zero to charge bank, draws the shortfall of 15kw from bank.
Under Application Settings, I have the max AC Input Power KW set to 3 (each inverter) so below the 10kw max I could draw. But it draws more than this limit.
I would expect this number to be the grand TOTAL that my inverter could ever draw from grid all inclusive.
I have AC charge enabled. and AC charge power is also set to 3 KW. So max battery charging should be limited to 9 kw for the total of 3 inverters.
Interestingly, below 10 kw total load, the inverters behave as expected. Meaning that if the load is 8 kw, then only 1 kw is used to charge batteries. If load is 3kw, then 6 kw is used to charge batteries. BUT as soon as load is 12k, then the inverters try to draw all of it from grid and none from battery bank. Not sure what to do.
So tech support suggested that the AC charge power for AC charge of battery bank is in ADDITION to the max AC Input Power KW set under the Application settings.
They suggested that I need to upgrade my grid to 25kw. But I will have the same problem as soon as my load goes to 26kw. It'll overload my grid and flip grid breaker. I would assume the same would also happen if grid was off and gen used instead. I'd hit a had top of maybe 18Kw for my generator. The answer here cannot be to get a 36kw grid connection and 36kw generator to match my max inverter output of 36kw.
Any help would be appreciated.
One solution I see is buying a 4th 18k inverter that just handles my grid and generator connection like my previous 3 Growatt inverters did.
So essentially:
Keep my 3 x 18kw EG4 and only connect them to Solar, battery and house.
They just supply the load, charge/discharge the bank using solar.
A 4th EG4 18k is ONLY there for handling my grid and generator inputs. It's only connected to Grid, gen and battery bank.
It does not communicated with the house, solar or the other inverters. (like my old setup above).
It reads SOC of battery bank. If SOC drops, it turns on grid just to "charge my battery" in the background. or fires Gen if grid is down to do the same.
The other 3 EG4s are none the wiser. They don't know anything and keep supplying the house with power no matter what, up to 36kw.
This setup worked well for me in the past. I'm tempted to repeat it, but with 4 x EG4 18k instead of 9 Growatt 5000 inverters.
Wow, long post.
I'm hoping there are just some settings I can tweak that will do this job for me with the existing 3 x EG4 18k that I already own instead of buying another one and adding it. But I will if there's no way around it.
In case you're curious why I would ever need that much load at all? Yes, I've loaded routinely in the teens and quite a bit in the 20s for charging my electric car, running all of our appliances and shop, etc.
Thanks,
Christian.