I am setting up a new EG4 - 18Kpu for my off-grid cabin and having a bit of trouble identifying the connections I need to make between the EG4 18K and the control wire terminal block on the Generac. I reached out to the guys at Signature Solar and their response after looking at the Generac wireing diagram is; "Unfortunately, we were not able to come to a conclusion on which wires you should be using. EG4 actually recommends that you contact the manufacturer of your generator for clarification as to what terminals C1 and C2, and which terminal is NC, C or NO".
Having read through some of the threads, it looks like for the EG4 18K, I need to connect a lead from GEN terminal to the '194 +12 VDC' terminal on the Generator, and from the NO terminal to the '0 DC Ground' terminal on the Generator.
Is this correct?
I appreciate the help.