{I see you don’t have a battery?
Not my understanding. Any battery SOC % below the AC Couple Start SOC value AC coupling should be disabled. I did test this out and it seemed to work like that as long as the start/end are not 100/255. So far I've only tested "off-grid".I see, AC couple start SOC value (mine 95%) is the ac coupled inverter start producing power when the battery gets down to 95%. So anything under 95% the AC coupling is working.
Test it and see, I was thinking the same way you are and someone on the forum straightened me out, they had a lot of patience with me. Please check that 255% I would not want your battery to get damaged.
AC Couple definitely does shut down when Battery SOC > AC Couple End SOC. So that's good.battery SOC at 60%. AC Couple Start SOC at 65%. AC coupling still running. What does the AC Couple Start SOC mean?
View attachment 247485
That is the value when you reset the inverter values to factory default! Wouldn't a better factory value be 95%?255% should be an illegal value, how did that get in there ?
That is the value when you reset the inverter values to factory default! Wouldn't a better factory value be 95%?
Actually it’s anything under 65% the ac couple will work and the battery will stop charging at AC Couple end SOC valuebattery SOC at 60%. AC Couple Start SOC at 65%. AC coupling still running. What does the AC Couple Start SOC mean?
View attachment 247485
There must be some off delay time, where the gen portI think I'm losing my mind. Battery SOC is at 60%. I had start SOC at 5% and end SOC at 95%. Gen port would not put out power. Waited several minutes. Then changed Start SOC to 90% and now the gen port puts out power. WTF? To start AC Coupling the AC Start SOC needs to be greater than Battery SOC?
Where do you get the 66% value from? 65% Start SOC + 1%? I assume. This is crazy.AC
once the battery hits 66%, as long as you are off grid. It should stop changing the battery.
Thanks, will read that a bit later.Post in thread 'EG4 18kPV Q+A general thread'
https://diysolarforum.com/threads/eg4-18kpv-q-a-general-thread.61636/post-957960
This is the post where y0bailey explains it to me
Now you're catching onThanks, will read that a bit later.
I wonder if AC Couple Start SOC is the SOC at which to start charging when the battery SOC drops *below* that SOC. So the AC coupling will charge the battery until it reaches the stop SOC and then not charge again until it drops below the start SOC. That seems to fit what I'm seeing. Making more sense now.
You would think so, but there are a few factory defaults that are wrong...50hz without a grid connection is another one.That is the value when you reset the inverter values to factory default! Wouldn't a better factory value be 95%?
Bare in mind there is a default 300 second timer before the switch, this can be changed.....but always changes back to 300 seconds if you change the grid profile.Waited several minutes. Then changed Start SOC to 90% and now the gen port puts out power
Yeah, I think it did not translate well from the dev lab to the general public.I wonder if AC Couple Start SOC is the SOC at which to start charging when the battery SOC drops *below* that SOC. So the AC coupling will charge the battery until it reaches the stop SOC and then not charge again until it drops below the start SOC. That seems to fit what I'm seeing. Making more sense now.
@altenergy21, I'm not sure what you mean by "chapter 2, Figure B." Can you give the name of the manual you are looking at and the page number? The user manual I am looking at, section 2 is the abbreviation list.
Is that page just a figure or does it actually have the settings needed to make it work? I know it "should" work. The issue is what exactly the settings need to be both for off-grid and on-grid to make AC coupling work.
For example. I am now testing off-grid. I can see the gen port power coming in and charging the batteries. There is nothing hooked to the load port of the inverter. AC Couple Start SOC = 100% and AC Couple End SOC = 255%. Current battery SOC is 55%. How is AC coupling charging the battery when the Start SOC = 100%? That makes no sense in my mind. There is no written, detailed, explanation of how this thing works. I would think that if the current battery SOC is less than the start SOC that the battery should not be charging, otherwise what is the purpose of the Start SOC??
So the issue is not a figure on how to wire it up or whether it should work or not, the issue is the actual inverter settings and how they affect the operation of the unit.
View attachment 247465