Samsonite801
Solar Wizard
- Joined
- Oct 15, 2020
- Messages
- 2,819
Ok, I have a neighbor who has one of the new 18kpv inverters, with 6 Lifepower4 batteries. All hooked up fine and working great for a couple days so far.
Then today they came over to my lot, and told me the power went off. I go and check it out, find that inverter keeps shutting off the inverter AC output relay the very instant I turn on the internal output breaker, sets the alarms seen in the title here.
For kicks, I test the ohms resistance on the output side property circuit and get about 900Ω which is far from a short, so I go out to all the circuits on the property, turn off all breakers, and the very last thing in the circuit left over was one RV plugged in with another extension cord in between. Turns out, it was the cause. Leave it unplugged and 18kpv is happy.
That RV works fine when the cord is plugged into a generator.
Now, I didn't have time to stay and keep troubleshooting tonight, was going to go back later and turn off all the breakers on that RV and turn them on one by one and try to isolate which circuit is causing the 18kpv to shut off it's AC output. Whatever it is, it is not tripping any breakers in the RV.
So here's my question (doing my homework before I go back over there), I am trying to figure out what those two alarm definitions are on the 18kpv.
'Trip by Vac abnormal'
'Trip by no AC'
The closest reference I could find on Google was from this Lux Power Tek manual, this inverter has the same UI, and lists those messages in the display screenshots, but in troubleshooting section it does not give descriptions about what those trips are or what causes them.
Perhaps someone else knows, or could help me find out what are the conditions or thresholds that trip these alarms?
Then today they came over to my lot, and told me the power went off. I go and check it out, find that inverter keeps shutting off the inverter AC output relay the very instant I turn on the internal output breaker, sets the alarms seen in the title here.
For kicks, I test the ohms resistance on the output side property circuit and get about 900Ω which is far from a short, so I go out to all the circuits on the property, turn off all breakers, and the very last thing in the circuit left over was one RV plugged in with another extension cord in between. Turns out, it was the cause. Leave it unplugged and 18kpv is happy.
That RV works fine when the cord is plugged into a generator.
Now, I didn't have time to stay and keep troubleshooting tonight, was going to go back later and turn off all the breakers on that RV and turn them on one by one and try to isolate which circuit is causing the 18kpv to shut off it's AC output. Whatever it is, it is not tripping any breakers in the RV.
So here's my question (doing my homework before I go back over there), I am trying to figure out what those two alarm definitions are on the 18kpv.
'Trip by Vac abnormal'
'Trip by no AC'
The closest reference I could find on Google was from this Lux Power Tek manual, this inverter has the same UI, and lists those messages in the display screenshots, but in troubleshooting section it does not give descriptions about what those trips are or what causes them.
Perhaps someone else knows, or could help me find out what are the conditions or thresholds that trip these alarms?