Issue resolved: forgot to check the zero export checkbox under advanced setting.
System Overview:
• Inverters: Two EG4 18KPV hybrid inverters (one primary, one slave)
• Battery Bank: 5x EG4 Power Wall Pro batteries in parallel
• Solar Array: Approximately two pallets of 440W solar panels shared between both inverters
• Power Panel: RV breaker panel with:
Issue Description:
• I’ve been using this setup in off-grid mode, and it has worked fine for continuous 300-400W loads on the 20-amp 120V outlet.
• However, I run into problems when connecting my Tesla Universal Portable Charger (UPC) set to 32A on the 220V plug:
• Current Limitation: The inverter maxes out at around 16-17A, even though I’ve set the charger to draw 32A.
• Overload Error: After about 30 minutes, the inverter triggers an off-grid overload (EPS overload) and shuts down.
• Lowering the UPC to draw just 9A still leads to this overload, despite the inverter’s 12,000W continuous rating (which should allow up to 50A at 240V).
Troubleshooting Steps and Observations:
• Time of Day: The overload occurs both during the day and at night, so it doesn’t seem related to solar input.
• System Capacity: The 12,000W continuous capacity suggests it should handle up to 50A at 240V, yet it overloads with far less.
If anyone has experience with similar issues or additional suggestions, I’d appreciate the input!
System Overview:
• Inverters: Two EG4 18KPV hybrid inverters (one primary, one slave)
• Battery Bank: 5x EG4 Power Wall Pro batteries in parallel
• Solar Array: Approximately two pallets of 440W solar panels shared between both inverters
• Power Panel: RV breaker panel with:
• 1x 50-amp 220V plug
• 1x 30-amp 220V plug
• 1x 20-amp 120V GFCI outlet
Issue Description:
• I’ve been using this setup in off-grid mode, and it has worked fine for continuous 300-400W loads on the 20-amp 120V outlet.
• However, I run into problems when connecting my Tesla Universal Portable Charger (UPC) set to 32A on the 220V plug:
• Current Limitation: The inverter maxes out at around 16-17A, even though I’ve set the charger to draw 32A.
• Overload Error: After about 30 minutes, the inverter triggers an off-grid overload (EPS overload) and shuts down.
• Lowering the UPC to draw just 9A still leads to this overload, despite the inverter’s 12,000W continuous rating (which should allow up to 50A at 240V).
Troubleshooting Steps and Observations:
• Time of Day: The overload occurs both during the day and at night, so it doesn’t seem related to solar input.
• System Capacity: The 12,000W continuous capacity suggests it should handle up to 50A at 240V, yet it overloads with far less.
- I’ve tested this same setup on both Inverters independently (on the master or slave inverter) and both inverters still trip the EPS/Off grip overload after a while supplying continuous of 2500-3000W charging the Tesla.
- I have also tried running my central Air conditioner, it was pulling 2200w and I do hear an oscillation struggle but it still kept the condenser running (just not smooth) leaving me think it did not supply sufficient amperage.
If anyone has experience with similar issues or additional suggestions, I’d appreciate the input!