DaveNSueM
New Member
Pulled trigger on EG4 18kPV - will be grid tied (already have interconnect agreement/net meter/local permits), NO backup load (have generator) and NO battery to start (future add)...pretty basic setup to start - a few pics/diagrams are attached. Service is 320a dual lug meter feeding house 200a load panel approx 150' underground and 100a pool/pavilion panel next to meter.
I was planning on supply side connection in 100a pool panel (via taps); however, utility has now said OK to adding 3rd lug in meter box and AHJ is happy with that too. Seems like a simple, clean connection method overall but would like opinions on this and a few other questions:
I was planning on supply side connection in 100a pool panel (via taps); however, utility has now said OK to adding 3rd lug in meter box and AHJ is happy with that too. Seems like a simple, clean connection method overall but would like opinions on this and a few other questions:
- Is the 3rd lug connection described above the best way to go with my setup design? Any downsides...other approaches to consider?
- In the described setup, where would I place the CT's...the 3rd lug PV grid line (which I am guessing would only sense PV production and see it as all going to grid) or the pool panel load lines even though that is minimal load?
- The house panel is where main loads are located; however, I do not have close access to those feeders - have been exploring posts on energy meter at house and routing back to inverted on RS485
- Any way to capture loads from both house and pool panel without adding a junction box at main panel to access the wires? Can inverter accept both RS485 input and direct CT input?
- Will inverter send to loads/grid without CT connected