ResonateSunshine
New Member
We are preparing to install EG4 18kPV to be mostly off-grid but using the grid bypass as back-up for now. We do not have any permits or inspections needed here in the country nor do we have a sell back agreement. I have attached image of wiring diagram from EG4 with some details from our system and questions I have. The main service breaker is on a pole near the garage shop ~100' from the house. There are loads for the shop in this panel but the breaker shuts off service to the house.
1. The EG4 notes say no load before feeder tap but there is no room to tap at the pole and would require long cable run. Can the tap still be done at the house service breaker?
2. For the same reason as above, can the CTs be located before the feeder tap in the house?
3. The diagram says 200 A breaker for the feeder but that the inverter can backfeed 50 A, should this be reduced to 150 A or lower? (Jesse Muller installed 70 A breaker after feeder tap
)
4. Wire Sizes need to correspond to breaker sizes. If 200 A grid-pass through, but EG4 load is only 50 A, should wires and breaker be full 200 A? Different than Muller install
5. Instead of manual transfer switch, plan to install interlock as EG4 apparently approved in Muller video, and main breaker off unless need to work on inverter.
6. Instead of just a PV isolater, considering retrofitting PV combiner box with a breaker for each PV string (details in diagram). The max ISC is calculated at 17.2 A and string max VOC at 586 V. Any issues with using 600 V 32 A breaker and 10 awg PV cable and labeling this box as PV disconnect 2 of 2?
7. EG4 will be installed inside. By installing RSD outside next to PV and labeling PV Disconnect 1 of 2, is there any need for 200 A non-fused disconnect?
8. Is the 6A 110V/3 A 240V stop switch sufficient for the RSD?
Thank you in advance!
1. The EG4 notes say no load before feeder tap but there is no room to tap at the pole and would require long cable run. Can the tap still be done at the house service breaker?
2. For the same reason as above, can the CTs be located before the feeder tap in the house?
3. The diagram says 200 A breaker for the feeder but that the inverter can backfeed 50 A, should this be reduced to 150 A or lower? (Jesse Muller installed 70 A breaker after feeder tap
4. Wire Sizes need to correspond to breaker sizes. If 200 A grid-pass through, but EG4 load is only 50 A, should wires and breaker be full 200 A? Different than Muller install
5. Instead of manual transfer switch, plan to install interlock as EG4 apparently approved in Muller video, and main breaker off unless need to work on inverter.
6. Instead of just a PV isolater, considering retrofitting PV combiner box with a breaker for each PV string (details in diagram). The max ISC is calculated at 17.2 A and string max VOC at 586 V. Any issues with using 600 V 32 A breaker and 10 awg PV cable and labeling this box as PV disconnect 2 of 2?
7. EG4 will be installed inside. By installing RSD outside next to PV and labeling PV Disconnect 1 of 2, is there any need for 200 A non-fused disconnect?
8. Is the 6A 110V/3 A 240V stop switch sufficient for the RSD?
Thank you in advance!