Thanks. My generator is pretty old, and I know it's pretty dirty.No. It's better.
Probably not.
The chargeverter was developed due to the piss poor chargers in the voltronics-like older line of EG4 inverter chargers - notoriously intolerant of even mildly dirty generator power.
The 6000XP is made by LuxPower and is more tolerant of dirty generator power.
Thanks. My generator is pretty old, and I know it's pretty dirty.
Umm, 625 KWHR?I have 2 6000XP's, 12K of solar, a chargeverter, 625KWH of basic Lifepo4 batts
Which would take 5 days?Now in a power-down scenario, I only run the gen long enough to pound 100A into my batts to full
That can’t be right, how did you determine that? I can measure it tomorrow but I’m guessing you’re off by two orders of magnitude.I did discover the Chargeverter, at idle, draws 250W on the AC input, just an FYI.
and it really wants to put the house load on the generator
That's how all inverter/chargers work. They can only do one at a time, so when charging from AC, they're passing it through to loads. That's why they recommend a generator 1.3-1.5X the size of your inverter, so you can meet rated loads while charging.
Ugh, I needed sleep last night, 625AH is what I meant (or 30kwh).It's a mixed-up pile of 6 100AH Chins 48V and 1 oddball 25AH I had bought for a UPS and threw in the stack instead. (Hence the relatively weird number)Umm, 625 KWHR?
Which would take 5 days?
That can’t be right, how did you determine that? I can measure it tomorrow but I’m guessing you’re off by two orders of magnitude.
Fair enough, that makes more sense.Ugh, I needed sleep last night, 625AH is what I meant (or 30kwh).It's a mixed-up pile of 6 100AH Chins 48V and 1 oddball 25AH I had bought for a UPS and threw in the stack instead. (Hence the relatively weird number)
As I mentioned earlier, I needed sleep last night... Anyways, 625AH of Batt (30Kwh), Obviously changes the math to about 6+ hours flat to full charge (assuming no other loads) and I use an eyedro on my mains to monitor grid use, that 250w is what I see in the monitor when I intentionally flipped the system to solar and had the CV as the only item on grid, I didn't believe it myself so I unplugged it, plugged back in. Sure enough, 250w is the idle draw on the CV. (I'm rounding up, eyedro reported .24kw)Umm, 625 KWHR?
Which would take 5 days?
That can’t be right, how did you determine that? I can measure it tomorrow but I’m guessing you’re off by two orders of magnitude.
I've learned that, as I was dealing with the Helene outage it did cause me a bit of frustration. The whole house ran fantastic on solar & battery all day, we didn't have to be careful, dryer, stove, A/C, it didn't matter, the EG4's ate it up without issue, all I really wanted from the Generator was to top-up the batteries before I went to bed, Solar took over reliably every morning (It was so unusual how clear and bright was the weather after that hurricane, ideal solar weather) I didn't have the chargeverter then (heck I didn't even have cell phone service to order one) and it just provided an extra challenge when I needed to charge (6-10pm I had to train the family to not turn on high-current stuff like the stove) as the gen was putting 60A into the batteries, stupidly designed generator has a fatal flaw of independent breakers on each leg, one would easily pop one and the whole system would just go crazy. The Chargeverter has obviously fixed my issues, which admittedly stem from a poorly designed generator.That's how all inverter/chargers work. They can only do one at a time, so when charging from AC, they're passing it through to loads. That's why they recommend a generator 1.3-1.5X the size of your inverter, so you can meet rated loads while charging.
Possibly? The eyedro is the usual inductive clamp style, I question it's accuracy below 1kw. I have some time later today to dicker around, I'll see what the fluke says.Not sure how accurate an eyedro is, but my Acrel measured about 53W (the red line) for _TWO_ CVGC boxes plus their grid relays, so maybe your eyedro doesn't take power factor into account (properly)? I was seeing a PF of about 0.145 with the CV output breakers off.
View attachment 259663
I had forgotten that the CV run their fans when they aren't loaded, so you (and I) were only off by one order of magnitude.
Remember that the Fluke may be measuring current and voltage, but unless you are accounting for power factor, you'll get a number about an order of magnitude high.Possibly? The eyedro is the usual inductive clamp style, I question it's accuracy below 1kw. I have some time later today to dicker around, I'll see what the fluke says.
Hi, I have 2 6000xp's also.... how did you connect your chargeverter to your batts? .... or maybe better question is where in the batt connections does the chargeverter connect?.... thanks... PaulieI have 2 6000XP's, 12K of solar, a chargeverter, 625KWH of basic Lifepo4 batts, and an older 12K Genset (super reliable, but non-inverter)
I learned after Hurricane Helene (7 days no power in SC) how bad you need a GOOD Inverter generator with the 6000XP, each one only has 30A of charger from A/C, and it really wants to put the house load on the generator, well it kept tripping 1 leg of my generator, which made the 6000 go absolutely nuts! I then decided to buy the Chargeverter, Now in a power-down scenario, I only run the gen long enough to pound 100A into my batts to full, the inverters know nothing and keep humming along happily. I'm doing other experiments with my system these days, trying to get every last KW out of solar and as little grid use as possible, As a sidenote, I did discover the Chargeverter, at idle, draws 250W on the AC input, just an FYI.
In the end, the biggest difference is 2 6000XP only give you 60A charger, The CV gives you 100A and will take the dirtiest 240VAC source you can find.
Reading this thread it seems not possible for an EG4 6000XP to charge batteries (from grid or generator) while providing power from inverter ? I noticed the 'Generator boost' option which seems to offer supplementing a weak generator with inverter power but I guess that is really the opposite (inverter would have to slave to the generator frequency/voltage).
I was hoping to configure the system so a generator could charge the batteries while the inverter was supplying loads but sounds like that may require a separate charger (eg Chargeverter) ?
Okay, well, the second sensible reason is if you have EXTREMELY sensitive equipment that doesn't handle the switchover between generator and inverting.