chadjones99
chadjones LLC
Question if someone could just verify what Im seeing. I have been running off of 1 x Eg4 6000 XP for the cabin for about 8 months. No issues other than once in a while we can overload 1 leg and the inverter would trip off line and reset ( maybe 2 or 3 times in 8 months ) I added a 4 kw load balancing transformer which did help a lot . We have just added a 2nd Eg4 6000 ( so we can run the well to pump up the sister tank without having to kill the breaker to the microwave,etc ) I got them tie together and are working. But here is what's weird to me the master inverter seems to be caring more of the load. example inverter 1 will show 40 % load and inverter 2 shows 22 % load. Then when we have inverter 1 at 75 % load inverter 2 showed 43% load. should they not show the same or close to the same load sharing ? ( I had turned off the breaker to the load-balancing transformer during the initial commissioning and testing. I did also breaker in the transformer not thinking I needed it but to see what it would do, it did not change anything as to the % load shared between the 2 inverters. I also notice that when all the heavy loads are off the inverters, inverter 1 shows 8 % and inverter 2 shows 6 % , so at the low end they are very close.
Is this normal is my question?
Is this normal is my question?