Leave the black where it's at and test the top of the Nader breaker.52.8 volts all 3 ares
Leave the black where it's at and test the top of the Nader breaker.52.8 volts all 3 ares
Are the breakers in the same position as they are in this photo? One off and one on? If they are both on and voltage is not being red at the top, but it's being read at the bottom, it could be a bad breaker or the breaker is installed upside down.
Got to go back to work, I’m a driver for the USPS, time to pick up bulk mailClass T fuse not reading going to breaker, on both side
How did you power on the inverter after the initial start-up?Both t class are both blown, on one side of rack only
He mentioned that he didn’t use the precharge resistors.How did you power on the inverter after the initial start-up?
That's what it looks like but you said you had voltage in the area circled in yellow?Both t class are both blown, on one side of rack only
How did you power on the inverter after the initial start-up?
How did you power on the inverter after the initial start-I have power the batteries up as recommended by signature solar, flip the Nader circuit breaker on ( 2 ) that I purchased from signature solar, then after doing so, did the pre charge that’s recommended for proper start up.
Did not fed ac power from the grid. Class t fuse is dead on one side and hot on the other. Tomorrow I will make sure I have a better connection, and retest.That's what it looks like but you said you had voltage in the area circled in yellow?
What do mean "on one side of the rack only"?
Hopefully it's only the fuses, the inrush current when you turned things back on could have caused it but we want to be certain before you replace them and try again..
You also said you isolated the inverters and fed them AC power but they wouldn't power on, correct?
Thanks for keeping the mail flowing, I bet it can be a fun job most days and miserable a few times a year...
That means the fuse is blown. Do you have replacements? Do you know what model the fuse block is?Did not fed ac power from the grid. Class t fuse is dead on one side and hot on the other. Tomorrow I will make sure I have a better connection, and retest.
200-300A T-Class Fuse (1X required for each 6500EX. The amazon listing stats that these T-class fuses are rated for 12V only. They are actually rated for 125VDC if you read the data sheet. By design, they could handle more than that. These are high quality fuses that will handle nearly any size LiFePO4 battery. This is what Will Posted YouTube channel.That means the fuse is blown. Do you have replacements? Do you know what model the fuse block is?
These may fit and would deliver quick but I can't guarantee they will fit your fuse block.
Again, we need to ensure the inrush current is what caused them to blow in the first place to rule out a potentially bigger issue.![]()
Blue Sea Systems Fuse JJN (Class T) 250 Amp 5118 - The Home Depot
Fast short circuit response makes this the best choice to protect high amperage electronics equipment such as inverters. 20,000 Amp Interrupt Capacity (AIC) UL rated for DC applications under UL189L. Product quality is managed in a manner consistent with international standards. Quality products...www.homedepot.com
200-300A T-Class Fuse (1X required for each 6500EX. The amazon listing stats that these T-class fuses are rated for 12V only. They are actually rated for 125VDC if you read the data sheet. By design, they could handle more than that. These are high quality fuses that will handle nearly any size LiFePO4 battery. This is what Will Posted YouTube channel.
Looking at one on Amazon-
Blue Sea Systems 5119 FUSE A3T (CLASS T) 300-AMP
They do go up to 400-AMP, I need to do more reading to see if it will fit the block. When I have my lay over today I’m going to bypass the fuse to the breaker to see if that was the issue, the fuse blowing. If not the fuse to continue the current from the batteries, if it doesn’t, the breaker is next in line as default.
Item model number | FBL-200 |
---|
we need to ensure the inrush current is what caused them to blow in the first place to rule out a potentially bigger issue.
Since I don’t have no “class T fuses” on hand this is what I did. I ran from the buss bar directly into the fuse box, on both sides so I could see if I could get current. When I went to the batteries to turn them on, the top one breaker on the battery flipped off, and I could smell smoke. So I turned the battery off and turned on the 2 blow it and the alarm red light comes on, on both of them .That means the fuse is blown. Do you have replacements? Do you know what model the fuse block is?
These may fit and would deliver quick but I can't guarantee they will fit your fuse block.
Again, we need to ensure the inrush current is what caused them to blow in the first place to rule out a potentially bigger issue.![]()
Blue Sea Systems Fuse JJN (Class T) 250 Amp 5118 - The Home Depot
Fast short circuit response makes this the best choice to protect high amperage electronics equipment such as inverters. 20,000 Amp Interrupt Capacity (AIC) UL rated for DC applications under UL189L. Product quality is managed in a manner consistent with international standards. Quality products...www.homedepot.com