Unless you have load between the Meter and the Gridboss.They are built-in. Shouldn't need remote CT's at all.
Unless you have load between the Meter and the Gridboss.They are built-in. Shouldn't need remote CT's at all.
Production meter between Meter and Gridboss will miss any self-consumption. As shown in the greyed box, PM goes between the EG4 Hybrid Inverter(s) and the Gridboss. May need:Folks,
EG4 will be publishing the following diagram on their website within a few days, but they have given me permission to share it early.
View attachment 256000
Notice the part I highlighted with the purple dashed line. It shows a way to deal with POCOs that insist on production meters and/or disconnects.
(I have asked for a version that shows only one inverter. I will provide it if I get it. However, I suspect it will be the same thing but without the combiner boxes.)
The gridboss has a bypass breaker that is interlocked with the load relay. This obviously does not completely isolate the GridBOSS, but it does take itself out of the picture functionally.
Yes, corrected the post.Do you mean FlexBoss 21s?
I don't know why either, but you never know unless they say it is ok.Assuming you do, I don't know why you could not AC couple a GlexBoss 21.
That's not how it should be setup. But I guess there might be some weird case for it. I don't know what that would be, or why.Unless you have load between the Meter and the Gridboss.
That's not how it should be setup. But I guess there might be some weird case for it. I don't know what that would be, or why.
Folks,
EG4 will be publishing the following diagram on their website within a few days, but they have given me permission to share it early.
View attachment 256000
Notice the part I highlighted with the purple dashed line. It shows a way to deal with POCOs that insist on production meters and/or disconnects.
(I have asked for a version that shows only one inverter. I will provide it if I get it. However, I suspect it will be the same thing but without the combiner boxes.)
Yes they will.I haven't seen it posted on any of the questions that I've seen.
Would the GridBoss work with 2 different EG4 hybrid inverters or do they have to be the same? For example, I have an 18kPV right now and want to add the GridBoss along with the FlexBoss21 (to save $$ over purchasing a 2nd 18kPV). Would they both be able to work together with the GridBoss?
Because, that's how they have always done it. (Change is hard)Can someone explain to me why it's any of the POCO's business how much solar you're producing? I don't understand the desire to have the meter as shown in the picture on page 4. (Between the gridboss and the inverter.)
Ug... so they essentially add and subtract to get what you actually owe? Seems pretty invasive to me.Because, that's how they have always done it. (Change is hard)
They haven't caught up with hybrid systems yet.
Before bidirectional metering was available. Two meters was the only way to do grid-tied metering.
This is the reason for the gridboss. It goes at the meter, and everything else can be remote mounted.Retrofit.
For example my inverter is in a shed 100 ft from my meter, and my main panel is another 70 odd ft from the shed. To use the grid boss i would have to replace over 180ft of buried wire with bigger wire, and replace the subpanel at the shed with a 200a one.
I wouldn't put electronic equipment outside in Texas, but that's just me, not saying it wouldn't survive.This is the reason for the gridboss. It goes at the meter, and everything else can be remote mounted.
That's an odd one. But I would think that you could wire the shed subpanel between the gridboss and inverter. This would avoid a second run of wiring.I wouldn't put electronic equipment outside in Texas, but that's just me, not saying it wouldn't survive.
but, walk me through what my "at-the-meter" retrofit would look like.
my main panel from the house( non backup) would connect to the non backup output of the grid boss. wire is already there so not a very big deal
the inverter in the shed would also connect to grid boss at the meter. wire is also already there so no big deal.
but then would I have to run a new another 100ft wire from the grid boss backup output back to the subpanel in the shed?
hmm that's an interesting possibility. so the 18kpv is feeding the grid boss through the backup output instead of the hybrid input?That's an odd one. But I would think that you could wire the shed subpanel between the gridboss and inverter. This would avoid a second run of wiring.
But I don't know if it would confuse the gridboss with missing power disappearing from what it thinks should be coming back from the inverter.
I don't know where that production information is pulled from. (The inverter or the gridboss)
Edit: I would probably need a rough sketch of your system, to know exactly how you are setup.
yes! this mix and maatch has succeed in testing and is pending releaseI haven't seen it posted on any of the questions that I've seen.
Would the GridBoss work with 2 different EG4 hybrid inverters or do they have to be the same? For example, I have an 18kPV right now and want to add the GridBoss along with the FlexBoss21 (to save $$ over purchasing a 2nd 18kPV). Would they both be able to work together with the GridBoss?
BTW: EG4 is starting to do these drawings for all of the inverters. You can find them under the downloads part of the web page for each product. (I don't know if all of the inverters have them yet but my understanding is that they will).He folks, EG4 just posted their one-line drawings for GridBOSS:
What you show is a split battery bank. (There is a setting to enable this). Each inverter will charge whatever batteries are attached to it.Maybe a dumb question...
If you have 2 FlexBoss21 units but one has 2 batteries and the other has 3, will we still use both inverters to charge all batteries?
Or does inverter 1 charge the 2 batteries and inverter 2 charge the connected 3 batteries? Seems like we cannot just connect all 5 together in parallel while having the bank of 5 connected to both inverters.
Please don't hit me too hard, I'm a noob!
View attachment 256125
If I understand your question correctly.... not really. The GridBOSS is the central part of an ESS System and as such is the central wiring point of the AC part of the system.question for @FilterGuy
Is there an easy way to remove the grid boss from service and still have power from the inverters?
Good Catch. I'll forward the feedback to the right folks at EG4The 18kPV diagram[1] and gridboss diagram[2] have different values for required breakers:
View attachment 256130
Says "For flexboss21 ... breaker to the gridboss needs to be 80 amps". And the table for breaker values goes up to 80 amps for the inverters.
View attachment 256131
"EG4 hybrid inverter breakers: FlexBOSS21: 90A" and the breaker value table is different.
[1] https://eg4electronics.com/wp-content/uploads/2024/09/EG4-18kPV-System-Wiring-Diagrams.pdf
[2] https://eg4electronics.com/wp-content/uploads/2024/11/EG4-GridBOSS-System-Wiring-Diagrams.pdf