James Showalter
CEO, EG4 Electronics, Signature Solar founder
You have to have a bypass and a fused knife disconnect, meter-main hasn't ever passed for our installers
The GridBOSS is service entrance rated so it should not have to have a separate grid disconnect. However, you should check with your POCO and AHJ. They sometimes have requirements over and above what the NEC would require.Hi all. I have a stand alone meter that sits between 2 200A service panels. I am backing up one service panel with an existing Enphase system, and I am now looking to back up the second service panel with PV, 12kpv, PowerPro and Grid Boss.
Because there is a 200A disconnect on the service panel that will serve as the backed up loads panel for GridBoss purposes, is it necessary to place a second disconnect after the meter but before the GridBoss Grid connection? I would assume yes, but want to confirm.
Thx.
I have been referring to that because Square D ads have been using thatCombination Service Entrance Device
Is it better to just call it a meter-main? I saw someone drop CSED a couple times in a thread and thought that might be the cool new GenZ way to call it
This is a good question for your utility / inspector.I have a meter outside with no exterior disconnect till the 200a house panel.... can I install gridboss indoors so the 200amp eaton breaker disconnect will be indoors? Also the rsd switch would be out doors right next to the meter
Service Disconnect/Emergency Disconnect (NEC 230.85) is supposed to be outside. The purpose is for emergency first responders to be able to quickly cut power.I have a meter outside with no exterior disconnect till the 200a house panel.... can I install gridboss indoors so the 200amp eaton breaker disconnect will be indoors? Also the rsd switch would be out doors right next to the meter
If the GridBOSS is acting as that, then it needs to be outside. If you have a separate SD/ED installed outside, then you don't need the Eaton breaker in the GB, which is why it is marked as "optional" in the maual. Remember, ground and neutral is bonded at the first point of disconnect and nowhere else, so that means SD/ED.For one- and two-family dwelling units, all service conductors shall terminate in disconnecting means having a short-circuit current rating equal to or greater than the available fault current, installed in a readily accessible outdoor location.
@FilterGuy is there output on the load port of the inverter (can i output to another panel or an EV outlet from there?)Folks,
EG4 will be publishing the following diagram on their website within a few days, but they have given me permission to share it early.
View attachment 256000
Notice the part I highlighted with the purple dashed line. It shows a way to deal with POCOs that insist on production meters and/or disconnects.
(I have asked for a version that shows only one inverter. I will provide it if I get it. However, I suspect it will be the same thing but without the combiner boxes.)

Yes there's still output to the load terminals on the flexboss.@FilterGuy is there output on the load port of the inverter (can i output to another panel or an EV outlet from there?)
View attachment 260095
@Adam De Lay : you said flexboss so can I assume the same for the Eg18 and eg12 ? so this output wont be recorded by the production meter ?Yes there's still output to the load terminals on the flexboss.
No, that's incorrect. From the GridBOSS manual (p. 26):Yes there's still output to the load terminals on the flexboss.
IMPORTANT: When operating an EG4 hybrid inverter with the GridBOSS, the inverter's load port will remain unused and should be in the off position. The inverter's grid port supports both grid input and output based on the inverter's settings. Critical loads will be cabled to and powered by the backup loads port on the GridBOSS.
No.@FilterGuy is there output on the load port of the inverter (can i output to another panel or an EV outlet from there?)
View attachment 260095
The load port on any inverter used to connect to the gridboss remains active. The comment in the manual is explaining how you wire up the gridboss because all your power and wiring should flow from the AC IN -> Gridboss, but it doesn't disable the load port on the inverter.No, that's incorrect. From the GridBOSS manual (p. 26):
@FilterGuy is there output on the load port of the inverter (can i output to another panel or an EV outlet from there?)
Thank you. That's...confusing. I assume he's talking about the inverter when saying "they're shorted together". So, essentially a double lug if hooked up like that?The load port on any inverter used to connect to the gridboss remains active. The comment in the manual is explaining how you wire up the gridboss because all your power and wiring should flow from the AC IN -> Gridboss, but it doesn't disable the load port on the inverter.
Yes, when he was talking about "shorted together" he was talking about the AC Output and AC Input connection. So they're both connected together and they would share the output capability.Thank you. That's...confusing. I assume he's talking about the inverter when saying "they're shorted together". So, essentially a double lug if hooked up like that?
Yeah it would be the same for the 18kPV or 12kPV.@Adam De Lay : you said flexboss so can I assume the same for the Eg18 and eg12 ? so this output wont be recorded by the production meter ?
thank you
My understanding is that you can have only one GridBoss and up to three hybrid inverters in your entire setup. The GridBoss can separate from the inverter and batteries but only one boss in the office.So just because I've got a weird configuration, and because it's useful to understand all the ways the GridBoss can be used, can I have:
In my 'power house', solar panels, inverters, batteries, a Grid Boss, the Utility Meter, and some loads, including Smart Loads.
_Way_ over there, 450 feet away, the main house with another Grid Boss, another inverter with batteries (maybe no panels, could be just an ESS to help with surges), and most of the other loads, including four (more) Smart Loads?
Does that make any sense?
According to a video from EG4, the issue with using aluminum is not that the connectors can't handle aluminum, it is that the connector size would have to be too large.The manual indicates only copper connections throughout the GridBoss. I currently have alumninm from the meeter into the main panel and to a 100A sub panel. I heard in an interview with an EG4 production engineer that said they "didn't have a problem with alumninum" but the 200A Eaton breaker would not fit some alumnimum conductor sizes. As I see it I have a couple of options.
- Opotion 1: Install my existing 200A breaker in a separate box then convert to coper and forego the GridBoss main breaker, connecting directly to the lugs. I would also need to convert back to aluminum to connect to the existing sub panel located in another building. Can I just use a properly sized 2-port multi-tap insulated connector to do this? Would I need to enclose this in another box or could I secure it behind drywall? If I go this route would the ground/common bond move to the first box with the single 200A breaker rather than in the GridBoss?
- Option 2: Install my existing 200A (Square D) breaker into the GridBoss and see what happens. I'm not worried about passing an inspection. In my area homeowners are allowed to work on almost anything without a permit or inspection (except the connection to the pole and septic tanks).
Any thoughts? Let me know if I am missing something. Sorry for the long post. Thank you.
- Option 3: See if the alumninm conductor will completely fit in the recommended Eaton breaker. If so
, Im sure nothing will start smoking.... right?

Do they still go around town with a horse and cart reading the meters?I was hoping the grid boss would qualify, but the POCO engineer said the disconnect switch needs to be the type that can be opened and visually see the contact points of the switch are disconnected/connected,
a normal breaker style disconnect is not sufficient.
Yup....The POCOs are slow to change. They require a LOT of things that are not in the NEC. If there was even a slight need for the big ugly 'visual' disconnect in order to be safe, it would be in the NEC.Do they still go around town with a horse and cart reading the meters?
No, but he got a little hot under the collar when I tried to explain that according to EG4 the gridboss was all I needed between the meter and service panel. Said you can never be completely sure it’s disconnected if you can’t physically see it.Do they still go around town with a horse and cart reading the meters?