In this video, Brayden from EG4 dives into Neutral-Ground Bonding scenarios and how they are affected by different use cases.
If you are no AC input then you bond the output.I feel like something a little clearer than a dry erase would be in order. I appreciate the effort on making this video. I personally am going to have to watch it a few more times before I understand and can apply this to my split phase 6500's with a Reliance transfer switch and no AC in but the neutral bonded at the panel.
So that means removing the screw from both my inverter's? Thanks again for bringing power to me and my family!If you are no AC input then you bond the output.![]()
Assuming you have an ac input for the grid and have installed the latest firmware. That’s what it sounds like.So that means removing the screw from both my inverter's? Thanks again for bringing power to me and my family!
Yes if the grid is present and you have a black terminal unit then the screw needs removal, grey terminal units have the screw removedSo that means removing the screw from both my inverter's? Thanks again for bringing power to me and my family!
You should have seen the system I used for my family 12 years ago as a teenagerSo that means removing the screw from both my inverter's? Thanks again for bringing power to me and my family!
That was the owner of SS.I also remember reading that someone from SS said that removing this screw hasn’t voided the warranty since 2020.
You could update firmware using the Mobile Firmware download.I saw this last night. Thanks for doing it. However, for someone like me, who has NO AC input on my off grid Eg 6000, which apparently DOES have the N-G bonding screw, it took HOURS of research to determine that since I had the N-G bond inside the unit, I did NOT need or want the N-G bond in the AC out sub panel that I build for items being powered by my inverter. Unfortunately, I see that the latest latest FW release, V 13, now "bypasses" the N-G bond screw. So now, IF I do the latest FW update, do I have to go reconfigure the subpanel and put a bond in the subpanel?? It looks like some of these patches or updates are being put out there, but may not be universally applicable to all units. At least the latest one has a cryptic change log advising that it bypasses the screw. Tom
Hopefully you are just saying this backwards?I have G/N bond in my sub panel before my main panel.
If you have a sub panel combining your inverters before going to your load panel and it is bonded then that is right.I have 2x EG4 6500. Split phase. I am completely off grid. No Inputs to either inverter.
One old model inverter w black terminal units. One newer one with grey terminal units.
I have G/N bond in my sub panel before my main panel.
So I have permission to remove the G/N bond screw in my older black terminal unit?
I believe this is the right thing to do, but I have heard I need permission from EG4 to do it so that I don’t void my warranty. I also remember reading that someone from SS said that removing this screw hasn’t voided the warranty since 2020.
Just want to make sure I’m doing the right thing here.
Hopefully just a terminology mistake.
Yes it’s exactly as James Says. Just a panel before my main house panel where the inverters combine, and also a place where I have the option to add in a generator backup.If you have a sub panel combining your inverters before going to your load panel and it is bonded then that is right.
The combiner panel connected to the AIO outputs (without inputs connected to grid) is your main panel. And the correct place for the N/G bond. Any panel after that is a sub panel. What used to be your main house panel, is now a sub panel. (Also known as the loads panel) neutrals and grounds should be separated there, now.Yes it’s exactly as James Says. Just a panel before my main house panel where the inverters combine, and also a place where I have the option to add in a generator backup.
Well now I'm really confused! I thought the main panel WAS the main panel and that's where the N+G bond lives.The combiner panel connected to the AIO outputs (without inputs connected to grid) is your main panel. And the correct place for the N/G bond. Any panel after that is a sub panel. What used to be your main house panel, is now a sub panel. (Also known as the loads panel) neutrals and grounds should be separated there, now.
In a grid bypass setting yes. In this case he is off grid. They were referring to the panel receiving power from the inverters in an off grid situation.Well now I'm really confused! I thought the main panel WAS the main panel and that's where the N+G bond lives.
It used to be a main panel.Well now I'm really confused! I thought the main panel WAS the main panel and that's where the N+G bond lives.
Can you send a picture of correct wiring for a sub panel combining two inverters and then feeding a main panel?If you have a sub panel combining your inverters before going to your load panel and it is bonded then that is right.