I don't think I'd actually want it to be fully automatic on shore power input though - As others have pointed out in this thread, if you plug into shore you want to disconnect your bond, but if you plug a generator into the same AC input you'd actually want to keep it bonded.
Generators come in two flavors: Bonded and Not-Bonded. Generators that come with a bond can usually be modified to remove the bond.
How the generator gets tied into the system is critical. If the relay circuit above is used and a non-bonded generator is tied to the gen port of a common neutral inverter everything will work properly.

However, if the generator is going to plug into the Shore power plug, the generator should be bonded (It should mimic shore power). It is typically pretty easy to add a bond to an unbonded generator.

Typically, if there is a shore/generator Auto Transfer switch I would expect the generator to be permanently wired (or at least permanently plugged in) As long as the generator has a permanent connection and it has an N-G bond, a 3-pole transfer switch can do the dynamic bonding for the RV.Although I see what you're suggesting actually in the second picture, this would require having separate inputs for gen/shore which I wasn't planning on.

It is a proposed circuit that has not been built. However, I did help a guy build something very similar for a 120V inverter and it worked well.Does someone sell a bonding relay box like this, or is this a proposed circuit to make?
Note that the links in the pic above take you to the parts on Amazon. Also, note that the terminal blocks are the most expensive component. You could build it for less by using a different wire connection method. Just make sure the connections are solid and can't vibrate loose.
- Don't use wire nuts
- If you use WAGO connectors, put tape over the levers so they can't accidentally pop open.
- Crimped connectors are best for mobile applications that will vibrate and bounce