@jharrell @1201 In my personal experience, due to the extremely clean transfer of the 15K, when switching from grid to inverting, you don't find out when the power goes off. That actually ends up being a problem, because people don't know to shut off high draw items, and they end up depleting their batteries!
True, actual experience of one of our customers..... Customers were meal prepping for guests that were there for the day, electric range was running, well pump for water, crock pot, water heater, etc. Power went off, but they didn't notice, as their power stayed on. (Great! Right?) All was great until right about when they were ready to eat dinner, then the whole house went dark. Batteries were empty. Luckily the food was hot and they had candles, so they ended up having a nice candle-lit dinner!
Same customer had power go off a few times where then their aux electric strips kicked in on the furnace (heat pump, with electric aux strips), at that point the 15K said "nope, I'm not capable of pushing 20,000W+" and shut down.
(This was pure oversight on our part. Fully aware of that!)
We ended up installing a "grid sense" relay that cuts the coil wires for the Aux heat strips to avoid that scenario. We also ended up installing (at the customers request) an indicator light that will turn on in their main living space, to indicate that grid power is off. That way they can limit their power draw.
Our conclusion has been that even though a single 15K can potentially work as "whole house backup" 99% of the time, it is possibly better to stick with critical loads panels if there is only a single inverter being installed.
Something else that factors into this whole picture as well is the fact that some of the local Utilities have a Level 2 interconnection threshold of 25kW, which means that installing 2x 15K's would mean more requirements in terms of paperwork and insurance coverage. Some don't even allow more than 25kW AC on interconnected solar for residential installs.