I can try that and see, wouldn't be to hard but the spec sheet for the inverter states that the DC voltage range is from 40 – 64 V (48 V nominal).The one chart show you are charging at 56 volts. This is at the limit for the normal 48 volts your invert is designed for.... I am thinking the unit is limiting itself because it is near its max voltage. Can you easily eliminate one cell group from your battery and try that?
Just ideas and trying to help. Good Luck.
I can try this, will have to wait till I have a morning to try this. I can say that I have did this when my power was out for 4 days, what I was getting is the same. Enphase will power my loads but always draws a little out of the battery. But when the Enphase power starts to exceed the load the inverter starts frequency shifting. What is disappointing with this is Schneider will no longer help me and they wont replace or return my inverter.Oats49250,
I have an idea for a little experiment for you.
Shut off all of the strings of Enphase, while the sun is still down in the early morning. This will cause all of the inverters to fully power down and reset.
Then run some load, about 1,000 watts or so, from the batteries through the XW-Pro. Once the batteries run down to below 54 volts, about 3.86 per cell or less, assuming you are running 14S, then turn on the breaker to just one string of the Enphase inverters.
Then watch the dashboard screen from the XW-pro. You should see the 1,000 watt load initially coming out of the battery to the XW-Pro, then going up to the house. Then as the solar comes online, after the normal 5 minute delay, the power going out should reduce by the amount the solar is producing. If the one string is not enough, it may still be consuming from the battery bank. Compare how much the flow to the house dropped to when the Enphase solar is reporting for energy produced. The Enphase Enlighten does not update for at least 15 minutes. Give it some time to actually get a graph, or open the Enphase installer toolkit and connect to the local Envoy. The toolkit gives a near live power being produced readout. I think you can also get that by entering the ip address of the Envoy into a web browser on the local network. I just tried this on mine and it shows "Production 1.02 kW at 8:41 am" right at the top pf the page, no login needed to see that.
Let it run like this, just one string for a bit and see what it does. As the sun comes up, your single string should start to produce more than your load, but if not, try adding just a second string. It will again take about 6 minutes before the inverters start producing. Try to use just enough panels to get it to charge instead of discharge. Watch the battery current and voltage. Ideally we want the current below what you set for maximum, and the voltage still more than 2 volts before your absorb voltage limit. That should stay running without frequency shift. If it does that, let it run for over an hour and then take a snapshot of the battery summary plot.
If things are acting up, and it keeps tossing the iQ7s offline, then there is a problem. If it stays online and charging, then add another string and see what happens. I really think you are just getting to a point where you are overpowering the XW-Pro and it has o limit the solar coming in. Let us know what this does.
I was told that the battery settings don't apply when running off grid ac coupled, so what settings could be causing the frequency to shift. I saw it shifting from 60.1 to 60.9hz. Using the CA grid profile and enabling state of charge in charge settings it went up to 5 amps. Because it kept changing to 60.1hz not all of the inverters would stay on, in the last try I had 32 inverters running. I thing only 9 were putting out power.
I was told that the battery settings don't apply when running off grid ac coupled, so what settings could be causing the frequency to shift. I saw it shifting from 60.1 to 60.9hz. Using the CA grid profile and enabling state of charge in charge settings it went up to 5 amps. Because it kept changing to 60.1hz not all of the inverters would stay on, in the last try I had 32 inverters running. I thing only 9 were putting out power.
The Enphase do frequency shifting, the problem is the Schneider shifts to much and shuts them down, instead of putting the power into my batteries.For my SMA string inverters, default frequency range is 59.4 to 60.5 Hz. That is the standard in-spec frequency range, so your microinverters shouldn't go offline below 60.5 Hz.
Start at that frequency (or higher), would like power output to ramp down with frequency. Mine are 100% at 61 Hz ramped down to 0% at 62 Hz.
If your microinverters do frequency-watts, there should be a similar range of frequency where they ramp down output.
There could also be frequency shift rate, Hz/second that the tolerate, and that the Schneider produces. My battery inverter takes several seconds to swing frequency, easy to watch with hand-held meter. It has to source/sink power while waiting or PV inverters to respond.
When I used a PV inverter that didn't respond correctly, frequency continued to rise until it was knocked offline, then frequency ramped back down.
So could there be a resistance problem? Could my resistance be to high? Can I measure that somehow?My thinking on this problem is that there may be a bad connection somewhere, or a BMS issue. Using the lower amount of power may show what is really going on. If there is a weak connection somewhere in the battery to inverter system, then the apparent voltage will climb with charge current. If the voltage goes too high, then the system goes into frequency shift as it sees the battery becoming full. Starting with a single string as the sun comes up should show if the system is stable as the power ramps up. Looking at the battery summary plot above, I do see the battery voltage changing nearly 0.5 volt for a 60 amps change in current. That works out to 0.008 ohms, or 8 milliohms, which does not sound too bad, but it is quite a bit more than my system is showing. Back when I had my power failure and it went off grid, it went from 23 amps charging to 18 amps discharging. That is a 41 amp swing, and the battery voltage only moved 0.17 volts. 0.17 / 41 = about 4 milliohms, and that was with just my single 360 amp hour battery bank and one JK-BMS handling all of the current.
The Enphase do frequency shifting, the problem is the Schneider shifts to much and shuts them down, instead of putting the power into my batteries.
Sub panel on the out side of my barn. That panel feeds my barn and my house. The wire size in that panel is 2 gauge feeding the Enpahse panel and the Barns panel. I have 4/0 feeding the house.Where are your micros tied into? Your main panel? or sub panel at the Schneider?
What are wire sizes in between the micro's and Schneider?