I purchased the Epoch 12460A-H and it just arrived.
I have an Epever Tracer 5415 Solar Charge Controller w/ MT50 programing screen. I've had it for about 5 years (with a VMax AGM) and am hoping to not have to buy another charge controller.
I want to make sure I have things configured correctly. I couldn't find anyone else on this forum who listed their settings for an Epoch, so I read the manuals and then called Epoch to talk to someone. They were very willing to help - but obviously had no experience with Epever. These are our best guess at settings, and I want to see if anyone else used the Epoch and Epever and had other recommendations.
Epoch Recommendations
From the website:
Voltage: 12.8V
Max Charge Voltage: 14.6V
Operating Voltage Range: 10.0 - 14.6V
Bulk/Absorption: 14.2V – 14.6V
Float: 13.4V – 13.8V
Equalization: 14.4V/ Disabled
Temperature Compensation: 0/Disabled
From the manual:
Follow these specified charging voltages to ensure optimal charging:
• Bulk Voltage: 14.2V
• Absorption Voltage: 14.2V
• Float Voltage: 13.6V
Best Guess at Settings for the Epever
Here are the settings settled on by the Epoch representative and myself:
Battery Type: User
Battery AH: 460
Temp Comp. Coeff: 0
Rated V: 12V
Over Volt. Disconnect: 14.6 V (must be > all other settings)
Charge Limit 14.5 V (must be >= Equalize)
Equal. Charge: 14.4 V (must be >= Boost Charge)
Boost Charge: 14.2 V (must be >= Float)
Float Charge: 13.6 V (must be >= Boost Reconnect)
Under Volt. Warn: 12.0 V
Equalize Time: 0min
Boost Time: 0 min
x -- Over Volt. Reconnect. 14.4 V - Not applicable because integrated load terminals are not in use.
x -- Boost Reconnect: 13.2 V - Not applicable because integrated load terminals are not in use.
x -- Low Volt. Reconnect: 12.6 V - Not applicable because integrated load terminals are not in use.
x -- Under Volt. Reconnect: 12.2 V - Not applicable because integrated load terminals are not in use.
x -- Low Volt Disc: 11.1 V - Not applicable because integrated load terminals are not in use.
x -- Discharge Limit: 10.6 V - Not applicable because integrated load terminals are not in use.
Does anyone else have an Epever and Epoch (or similar battery) and want to critique my settings?
Thanks.
- Josh
I have an Epever Tracer 5415 Solar Charge Controller w/ MT50 programing screen. I've had it for about 5 years (with a VMax AGM) and am hoping to not have to buy another charge controller.
I want to make sure I have things configured correctly. I couldn't find anyone else on this forum who listed their settings for an Epoch, so I read the manuals and then called Epoch to talk to someone. They were very willing to help - but obviously had no experience with Epever. These are our best guess at settings, and I want to see if anyone else used the Epoch and Epever and had other recommendations.
Epoch Recommendations
From the website:
Voltage: 12.8V
Max Charge Voltage: 14.6V
Operating Voltage Range: 10.0 - 14.6V
Bulk/Absorption: 14.2V – 14.6V
Float: 13.4V – 13.8V
Equalization: 14.4V/ Disabled
Temperature Compensation: 0/Disabled
From the manual:
Follow these specified charging voltages to ensure optimal charging:
• Bulk Voltage: 14.2V
• Absorption Voltage: 14.2V
• Float Voltage: 13.6V
Best Guess at Settings for the Epever
Here are the settings settled on by the Epoch representative and myself:
Battery Type: User
Battery AH: 460
Temp Comp. Coeff: 0
Rated V: 12V
Over Volt. Disconnect: 14.6 V (must be > all other settings)
Charge Limit 14.5 V (must be >= Equalize)
Equal. Charge: 14.4 V (must be >= Boost Charge)
Boost Charge: 14.2 V (must be >= Float)
Float Charge: 13.6 V (must be >= Boost Reconnect)
Under Volt. Warn: 12.0 V
Equalize Time: 0min
Boost Time: 0 min
x -- Over Volt. Reconnect. 14.4 V - Not applicable because integrated load terminals are not in use.
x -- Boost Reconnect: 13.2 V - Not applicable because integrated load terminals are not in use.
x -- Low Volt. Reconnect: 12.6 V - Not applicable because integrated load terminals are not in use.
x -- Under Volt. Reconnect: 12.2 V - Not applicable because integrated load terminals are not in use.
x -- Low Volt Disc: 11.1 V - Not applicable because integrated load terminals are not in use.
x -- Discharge Limit: 10.6 V - Not applicable because integrated load terminals are not in use.
Does anyone else have an Epever and Epoch (or similar battery) and want to critique my settings?
Thanks.
- Josh