Hi guys.
Need some advice on the following system: Growatt Inverter MIN3600TL-X and Canadian Solar 655W panels.
Growatt specs:
Max. input current per MPP tracker: 12.5A
Max. short-circuit current per MPP tracker: 16A
Max. output current: 16A
PV system: 6 x 655W panels in series
Short Circuit Current (Isc) : 18.43 A
Opt. Operating Current : 17.2 A
Is it safe to exceed inverter input current? If not what would be the alternative, considering the inverter must be grid-tie and they are all around 12.5 A per input?
If safe, would there be a huge loss in performance?
I have attached some files with specs.
Thank you