I have what I think is a dumb question regarding grounding and lightning protection, the SCC GFP system, and my combiner boxes. This is a case of thinking I knew what I was doing, getting the stuff, and going 'wait, how does
this fit...'
I have reviewed
filterguy's document on grounding and his document on
solar panel ground fault protection systems. I believe page 4 of his GFP document most closely matches my system.
This is my system diagram:
This is my
combiner box:
My SCCs are Midnight Solar Classic 150s, which I'll run in Follow-Me mode. I intend to use the internal GFP setup. Per the SCC manual, p18:
"If the internal grounding jumper is installed in a Classic [what you do when you are using the unit's GFP system], the battery negative and DC source negative must not be connected to the system grounding conductor anywhere in the system. Grounding of these circuits will defeat the GFP function."
My read of that statement is:
- At no point outside of my master SCC do I connect PV negative or battery negative to ground.
- At my master SCC, the PV and battery negative will connect to the internal grounding jumper. I will run ground from that jumper to my main ground at the AC panel (which is a ground wire bound to metal water pipe, I believe).
- The bare copper ground wire I'm bonding to my PV panel frames and rack will run all the way to that single ground point (or, because of the layout of my equipment room, I'll connect it proximately to the master SCCs internal grounding jumper).
Okay, that seems simple enough. My diagram reflects this. (Although, is it correct that I'm taking the DC ground to the inverter DC ground lug, or should I be wiring the DC ground directly to the earth ground near the AC panel where it's grounded to a pipe? I'm seeing conflicting things on different diagrams, and I don't understand the relationship between the inverter DC ground lug and the AC ground. Are they connected electrically? I think so, but I'd rather not assume and the manual doesn't say.)
Okay we're getting to my question. When I look in that combiner box, there's a ground wire connection coming out of the bottom of the arrester, the blue device on the right. You can see some examples of this in
this thread on these style combiner boxes, and here is a screenshot of a pic wattmatter posted there:
What do I do with that? Isn't that ground wire connected to the PV negative, and thus a no-no per the SCC's GFP system?