I have a fuse between the solar charge controller and battery. I also have a kill switch between the SCC and the battery. I also have breakers on the PV side between the panels & SCC.
There was no load running on my inverter (2000 W) or the battery (12V LiFePO4 Chins 200Ah). The sun charged up my battery to over 14.2 Volts, and the inverter was making noise (overcurrent alarm - renogy product).
I went outside, and turned on a 12V load. I looked at the SCC and it said 19 V, which is what the solar array (300 W, 2 panels) brings in to the SCC.
I looked at my battery monitors that connect to the PV input and side of the SCC, and the one on the negative battery terminal. Both read 19.1 V!
I immediately killed the breakers on the PV side, and killed the connection between SCC and Battery as well. Voltage dropped down to 14.5.
I started up a 12V load (small - 50 watts max) and the beeping of the inverter stopped and voltage relaxed down.
So a few things:
1. - pretty sure I have a bad solar charge controller
2. - if the shunt and monitor on the battery side said 19 V, why didn't the battery internal BMS stop it at 14.6 or something?
3. - Was my battery monitor just showing that 19V was coming INTO the battery, but the battery itself was not more than 14.5 V? Battery does not have bluetooth.
4. - Did the battery BMS actually prevent the 19V, but I could not see that? Asking because why when I killed the SCC power line to the battery (after PV was killed) did the battery drop from 19V down to 14.5 so quickly?
5. - If the SCC doesn't prevent more than 14.4 or whatever voltage from going to the battery, what is supposed to do that?
6. - Is the SCC junk now, or can I add a victron battery smartconnect or whatever its called to kill it instead of the SCC?
7. - I have had something similar to this happen on another SCC with a different battery. I threw that SCC away. The battery was fine, however I was scared. I think sending 19 V - like straight from a panel - to a battery can make things go boom or catch fire.
8. - The glass fuse I had did not blow - it blows based on amps, not volts I guess.
9 - I need to get a kill switch between the positive or negative battery cable, not the SCC and the battery. I am using 4/0 wires, so finding a kill switch that is affordable may be a challenge.
Thank you all SO MUCH for reading! SCC and PV still disconnected; battery running a small DC load to drain it down just to be safe.
There was no load running on my inverter (2000 W) or the battery (12V LiFePO4 Chins 200Ah). The sun charged up my battery to over 14.2 Volts, and the inverter was making noise (overcurrent alarm - renogy product).
I went outside, and turned on a 12V load. I looked at the SCC and it said 19 V, which is what the solar array (300 W, 2 panels) brings in to the SCC.
I looked at my battery monitors that connect to the PV input and side of the SCC, and the one on the negative battery terminal. Both read 19.1 V!
I immediately killed the breakers on the PV side, and killed the connection between SCC and Battery as well. Voltage dropped down to 14.5.
I started up a 12V load (small - 50 watts max) and the beeping of the inverter stopped and voltage relaxed down.
So a few things:
1. - pretty sure I have a bad solar charge controller
2. - if the shunt and monitor on the battery side said 19 V, why didn't the battery internal BMS stop it at 14.6 or something?
3. - Was my battery monitor just showing that 19V was coming INTO the battery, but the battery itself was not more than 14.5 V? Battery does not have bluetooth.
4. - Did the battery BMS actually prevent the 19V, but I could not see that? Asking because why when I killed the SCC power line to the battery (after PV was killed) did the battery drop from 19V down to 14.5 so quickly?
5. - If the SCC doesn't prevent more than 14.4 or whatever voltage from going to the battery, what is supposed to do that?
6. - Is the SCC junk now, or can I add a victron battery smartconnect or whatever its called to kill it instead of the SCC?
7. - I have had something similar to this happen on another SCC with a different battery. I threw that SCC away. The battery was fine, however I was scared. I think sending 19 V - like straight from a panel - to a battery can make things go boom or catch fire.
8. - The glass fuse I had did not blow - it blows based on amps, not volts I guess.
9 - I need to get a kill switch between the positive or negative battery cable, not the SCC and the battery. I am using 4/0 wires, so finding a kill switch that is affordable may be a challenge.
Thank you all SO MUCH for reading! SCC and PV still disconnected; battery running a small DC load to drain it down just to be safe.