Then why are the manuals recommending 4 awg? With proper connections.or you could make the connections properly to the device then #6 would be fine
Also had some people say that you can use six awg. But that's not recommended:
View attachment 279707View attachment 279708
I always install these with 4 awg unless it's on the concrete wall of the bunker. Better safe than sorry.
If it's set to 40A you're good with 6awg. And thank you!I wired mine with 6-gauge THHN for a 40-foot run for my EV charger outlet. That was to spec. We have two EV's... a Ford lightning and a Nissan Ariya and have been charging both for 1 year now. My 14-50 outlet is a heavy-duty model that has an Emporia Stage 2 EV charger plugged into it, note that it is set internally to only operate at 40A on a 50A rated outlet. The wire run is underground to a metal RV cover, all outside away from anything flammable. After 1 year of use on 2 EV's it hasn't shown any issues. I did inspect the inside about 6 months in with no noticeable concerns from that inspection.
I did watch a YouTube video (several actually) a year ago about using the cheapo dryer plugs on EV chargers... and that is a NO-NO. You need to get an outlet that is beefy and rated for continuous use, especially when using for EV charging.
Love all of your hard work and video's Will! Thank you for leading the charge!
Best regards,
John
Technically, according to NEC 110.3(B), you need to follow manufacturers instructions. The more restrictive wins, so if wiring amp tables say #6 and Tesla manual says #4, code says you need #4. (Doesn't work in reverse.)Then why are the manuals recommending four awg? With proper connections. Are all the engineers at Tesla just complete idiots or something? Can you substantiate your reasoning with evidence?
You can't pull 50A continuous through a NEMA 14-50. That's why chargers that are made to plug into them top out at 40A. 48A chargers need to be hard wired to a 60A circuit.6 AWG works great for continuous 40A.
Need 4 AWG if you are pulling 50A Continuous. With charger or plug. Most manuals state that even with 4 AWG, you can only use 40A with a plug between the charger and breaker.
Need hardwire 4 AWG to pull 50A all day long without issue.
Yes agreed, but I have found that the industrial rated Hubbell is rated for continuous 50A. But as I said above, the manuals for the chargers say that 40A is maximum. Thought I should mention both.You can't pull 50A continuous through a NEMA 14-50. That's why chargers that are made to plug into them top out at 40A. 48A chargers need to be hard wired to a 60A circuit.
Also you only actually need 8 AWG copper THHN for a NEMA 14-50 plug (although I'd typically use 6 AWG anyways). Anything 8 AWG and larger can use the 75C ampacity column as long as both wire and terminations support it.
This. People forget the 120% rule where the components of a circuit need to support 120% of the rated load. A 40A device needs 48A wire, receptacle, and breaker. Since they don't make 48A parts you need to step up to 50A.You can't pull 50A continuous through a NEMA 14-50. That's why chargers that are made to plug into them top out at 40A. 48A chargers need to be hard wired to a 60A circuit.
Also you only actually need 8 AWG copper THHN for a NEMA 14-50 plug (although I'd typically use 6 AWG anyways). Anything 8 AWG and larger can use the 75C ampacity column as long as both wire and terminations support it.
You'd have to hook it up to a 50A continuous rated breaker too which isn't standard for residential panel breakersYes agreed, but I have found that the industrial rated Hubbell is rated for continuous 50A. But as I said above, the manuals for the chargers say that 40A is maximum. Thought I should mention both.
Now that's a good forum post. Nice. Good points.Theres a lot of details improperly cited in here.
First of all, there is the wall connector and the mobile connector.
Wall connectors - G3 is rated to 48A max. 125% rule needs 60A breakers. 6awg is fine if breakers are 75C. 4awg if on 60C breakers.
Gen 1 and gen 2 wall connectors are up to 80A. 125% is 100A breakers. 3awg.
Mobile connectors max is 40A, 125% is 50A breakers.. 6awg all day long.
Im on mobile so can't cite the whitpapers, but anyone can go to tesla and download each data spec.
Tesla makes no rcommendation re 4vwg or 6awg, defers to local codes.
Best tobsupport the mobile charger cord , it's not good to have the plug move at all. Theres an insertion cycle count rating.
I have gen 2 wall connector at 32 amps, = 40amp breaker. Also redid all the wiring up and down my neighborhood for free. Always 6awg at 48A max and always hubble brands.
When I installed my Tesla hardwire Universal Wall a charger last year, 6awg thhn was recommended. The wires and EMT get warm but never hot to the touch at 48amps with 60amp breaker.6 AWG works great for continuous 40A.
Need 4 AWG if you are pulling 50A Continuous. With charger or plug. Most manuals state that even with 4 AWG, you can only use 40A with a plug between the charger and breaker.
Need hardwire 4 AWG to pull 50A all day long without issue.
If 30A, 8awg is really ok. The receptacle contacts on those cheap 14-50s are far inferior too. Then if one is using a mobile type plug that gets plugged in/out at various locations, the plug eventually gets fouled and is then introduced to the home receptacle.I'm using one of those cheap-o 14-50 outlets that Will cited in his video. While I don't think the outlet is my only problem, I'm going to replace it.
My 2019 Nissan Leaf SV+ will supposedly draw no more than 30 amps. 6.6kW / 240v = 27.5 amps. Wire gauge calculators said I could get by with 8 gauge for the distance. The outlet is getting warm. The EVSE plug has a sensor in it that detects the temperature. Mine has gone into fault mode due to high temperatures a couple of times. I'll start by replacing the outlet and then stepping up to 6 gauge wire.