Thanks for the info. I really appreciate it. I am new to this. I plan on keeping the inverter off most of the time and only turn it on if/when necessary. I primarily want to keep my 2 - 100amp Battle Born batteries charged.
Here is the link to the bus bars. I wasn't aware there were so many different options.
https://www.amazon.com/Mofeez-Power...pd_rd_i=B09J23SRCW&psc=1&ref_=pd_bap_d_rp_1_t
That definetly is a brass busbar. Some may use this, but I avoid it. I did purchase a brass busbar, but I never installed.
This switch will be at the advertised limits with your equipment.
I’m a bit skeptical of its limits though. Starts out claiming it is 48 volts 475 amps, but then further down you see its momentary, and also hidden is a 275 amp rating. The more you operate towards the 2000 watt limit of the inverter, the less comfortable I am with this switch. I have what is probably the same switch, but from a different vendor, but on a 24 volt install that sees 40 amps tops.
I am using 2 guage from the battery to inverter and 8 guage for the solar charge controller. I don't think I could get any larger cable into the solar charge controller.
The SCC will be fine. Check the ampacity of the wire You have. A 12 volt inverter with a low voltage cutoff of 10 volts and accounting for a 15% coversion loss could easily approach 250 amps. I kind of doubt your 2 AWG is rated for that. The spec sheet for that particular wire and manufacturer will say.
I really appreciate any tips. I connected it to one of the batteries today just to see if everything came on which it did but want to make sure everything is correct. Thanks again!!!!!!!
Electricity does scare me. Over 100k+ electrical fires a year in the US.
I have a 3000 watt 24 volt inverter on my RV and I took many precautions building that. As close to code as I could get especially seeking UL listings for components. For a 300 watt solar generator, I was not so careful. The difference for me is the 300 watt generator does not run close to my house so if it burns down, so if there’s a problem I only use the generator.
To me the more these builds are actually used, the more attention has to be paid.