First off, thank you to everyone who posts on this site and for the people who have been helping me so far.
I am learning a huge amount. So much that I might be getting myself confused lol.
We have a 320 sq. ft. off-grid cabin with a Jayco 29' camper on site and would like to go solar.
The plan is to spend 3 or 4-weeks and then a bunch of weekends at the cabin. Probably around 40-45 days or nights a year.
We plan on using our 2 Honda 2200i generators, which can be run in parallel, for our initial energy needs and charge a battery storage system when the sun isn't shining enough.
I used snoobler's excel spreadsheet, which was great, but not sure if my numbers are accurate.
Here is my first attempt at a design. Let me know if I am heading down the right path or not:
Even though I entered 2-days of energy storage, I am fine with 1 day and using generators as-needed.
Considering this setup:
Thank you for all the help.
AJ
I am learning a huge amount. So much that I might be getting myself confused lol.
We have a 320 sq. ft. off-grid cabin with a Jayco 29' camper on site and would like to go solar.
The plan is to spend 3 or 4-weeks and then a bunch of weekends at the cabin. Probably around 40-45 days or nights a year.
We plan on using our 2 Honda 2200i generators, which can be run in parallel, for our initial energy needs and charge a battery storage system when the sun isn't shining enough.
I used snoobler's excel spreadsheet, which was great, but not sure if my numbers are accurate.
Here is my first attempt at a design. Let me know if I am heading down the right path or not:
Minimum System size calculations | ||
Full Load Wattage | 3158 | Watts |
Full Load W-hrs. | 7152 | W-Hrs. |
Full Surge wattage | 1075 | |
Inverter efficiency | 96.00% | % |
Full Load Inverter size (input watts) | 3290 | Watts |
Full Surge load Inverter size | 44 | Watts |
Daily Storage Requirement | 4000 | W-Hrs/Day |
Max discharge from full CHARGE | 90.0% | % |
# days of storage capacity | 2.0 | Days |
System Voltage | 48.0 | Volts |
min Battery capacity W-Hrs | 8888.9 | W-Hrs. |
min Battery capacity A-Hrs | 185.2 | Amp Hours |
Max continuous current from bat. | 68.5 | Amps |
Max Continuous discharge rate | 0.37 | C |
# sunny days to recharge while under load | 1.0 | Days |
Required Total daily Solar output (Sunny) | 8000.0 | W-Hrs. |
Insolation # (Equivelent hours of full sun) | 4.0 | Hours |
Min Solar Cell Wattage | 2000.0 | Watts |
Max Charge Current | 41.7 | Amps |
Max Charge rate | 0.22 | C |
Even though I entered 2-days of energy storage, I am fine with 1 day and using generators as-needed.
Considering this setup:
- 5 panels - Q.PEAK DUO L-G8.2-430 (430 Watt Mono G8) 24V
- HYBRID LV5048 Split Phase 120V/240V output 5kW 48V, Dual 4kW Solar MPPT inputs (8kW)
- 2 - SIMPLIPHI POWER PHI 3.8KWH LITHIUM (LFP) BATTERY, 48V
SimpliPhi Lithium Deep Cycle Batteries
SimpliPhi Lithium Ferro Phosphate (LFP) Deep Cycle Batteries are safer than lead acid batteries with a much longer cycle life.www.altestore.com
Thank you for all the help.
AJ