Difficult to say, when exactly this occurred. It seems like it was gradual over time. My system runs just during the day to maximize solar. The three batteries are there to smooth everything out. Between solar and battery it’s between 10 to 30 kW. But one day it just didn’t turn on and I noticed this.What was the load pulled from/to the batteries?
Have you seen the manual?And were they nuts torqued to spec?
I followed the manualThat only occurs if there is resistance, commonly caused by not properly torquing or bad crimps. In this case there are no crimps, so that can be ruled out.
I also seem to see a washer BETWEEN the busbar and the fuse. Thats #1 fail and will create heat for sure.
Nuts/washers are to secure the connection, NOT to be part of the conductive circuit
can you clarify if you’ve seen the manual?Imho it does more look like an installer/builder fault (they are DIY kits) and not a mfg risk/failure.
did I misinterpret this photo:View attachment 193476
Was there anything mentioned about this in the manual how to assemble the pack? If not so they should include this.
There are no washers here nor is this how it was. I loosened these intentionally when I took it apart because the pop on terminal was melted and I needed to use pliers to get it off. I didn’t want to bend this just in case.Edit: It seems the same is the case between busbars and the front terminals. That also will heat up. Won't be surprised if the positive terminal (partially) has melted as well.
Can't see it clearly but it does look there is space there as well, indicating maybe a washer there?
Check all connections, also on the negative. There should NOT be any washers between conducting surfaces.
View attachment 193478
Gotta take what you can hahaOn an upside looks like that 400a fuse held, lol!
Can you clarify what you are talking about the BMS was bypassed? I built it following the manual. Did I miss something?Wow.
Several issues here...
Looks like the bms was bypassed...
Half the current path ignored, and a scary amount of power was being pulled.
I hope OP responds with photos and explanations of the build before failure...
Yeah, be careful with the manual.I'm thankful to see this. I haven't built yet, but was looking at that Apexium, and now I'm getting the benefit of learning more from others' mistakes. So thank you for posting this! I may not have made this mistake, but I might have, too, as I wasn't realizing the importance of keeping washers out of the current path.
I think I would have followed that photo the same as you did. It does appear to have an in-current-path washer on each side of that connection, and I would have thought, looking at the photo, that the washer was suggested there to raise the bar above the level of the adjacent insulating material. Obviously, if the bar managed to pinch some of that insulation, it would not make a good connection. But that insulation may be just past the ends of the bar...I'm not sure how well the graphic portrays the actual setup.did I misinterpret this photo:
I’m learning and that’s something that if it’s shown in the manual, I’m going to duplicate it. Glad to know that now thank you.Unfortunately I see a lack of understanding of how to assemble high power electronics.
No washers in the current path, double check all connections including several days after running with load etc.
My battery kits wanted washers in the current path too but mine were copper/brass and I limited them to where absolutely necessary.
There were some height issues with the fuse holder/BMS and bus bars that need to be addressed. Or replace the fuse with a CB.
Also, looks like it may have got wet on the front panel and that + connector is toast.
Let us know if you see anything else if you do review the manual. I have two additional batteries and I want to fix. Which ones were you saying to remove?I haven't seen the manual, I only made conclusions based on the images you've provided.
I agree the images you posted DO look there is a washer between the busbar and the fuse, which is wrong, unless they are 100% conductive like copper.
I'll check the manual (getting curious now) later this evening (its 3pm over here), since it seems there are mistakes in the manuals. I think Apex should improve/correct that off course since they will pose a high risk when pulling massive amps.
Can't blame for that since it seems to be wrong in the manual in the first place, which is only Apex to blame. If you're not familar with high currents, its not that uncommon to follow a manual (which is better than just doing something!)
And sorry for beeing too harsh, since you HAVE used the manual, only that one includes wrong information! Too bad you need to have this close call to find out.
Yes, the fixed nut is called a PEM nut typically, made by PEM technologies. I used them daily at work. These ones are Zinc Plated Steel, and definitely NOT good for conductivity.Couldn't resist looking into the manual and I agree with @Lt.Dan note about the terminals.
The manual is, imho, wrong here. To me, the busbars should make direct contact to the terminals busbar, and the current should NOT be passing the (fixed) nut. That nut/thread is only to secure the bolt.
That busbar should be mounted exactly the other way, so the bar from the fuse makes direct contact with the busbar towards the terminals.
NOT as in this image where the supporting nut is part of the circuit.
View attachment 193505View attachment 193507
As for the washers: Remove washer C. So the fuse is in direct contact with the busbar. The washers on both sides should 'sandwich' the busbar/fuse, but not be in beween.
I'm quite certain he means for the one labeled "C" in your image to be removed. You want the increased surface area of the contact between the bars, without the added resistance of the washer itself, which is not designed to be an especially good conductor.Which ones were you saying to remove?
So the female wire terminal was melted to the male. I had to snap it off with pliers and I didn’t want to risk bending this metal inside. Can you see this photo for how it looks tightened and if correct?View attachment 193501
Whether it's in the manual or not, this picture that was posted above needs to be addressed as well, the bus bar needs to go to the top of this copper bus bar, not the Zinc-Plated Steel PEM nut. I saw this when assembling my 3x Seplos cases and it's very easy to make this mistake.
I assembled 3x of the Seplos cases (which are exactly the same) and didn't have manual, so I haven't read it either.
Can you clarify the positioning a little more?Couldn't resist looking into the manual and I agree with the note from @Lt.Dan about the terminals.
The manual is, imho, wrong here. To me, the busbars should make direct contact to the terminals busbar, and the current should NOT be passing the (fixed) nut. That nut/thread is only to secure the bolt.
That busbar should be mounted exactly the other way, so the bar from the fuse makes direct contact with the busbar towards the terminals.
Got it thanksNOT as in this image where the supporting nut is part of the circuit.
View attachment 193505View attachment 193507
I found a picture in another Apexium thread:
This is how it should be in my opinion, not as in the manual
View attachment 193510
As for the washers: Remove washer C. So the fuse is in direct contact with the busbar. The washers on both sides should 'sandwich' the busbar/fuse, but not be in beween.
Will a heat laser work?Current is passing the main circuit, busbar on busbar / terminal / fuse. Bolts/nuts/washers are to secure it in place. If there is no other way, use suitable conductive materials. Regular (steel/rvs) washers eg aren't.
When in doubt (And I personally always do on high current installs), run it for 15-30min and check with a flir camera. Any bad connection/resistance will show up very clearly.
I hope I don’t have to buy anything and Docan makes me whole. What a shit show. I need to get this up and running today even if it’s a short temporary workaround. Any ideas of parts that I can run into town instead of waiting for shipping?I think the busbar only has gotten very hot. Carefully clean, (very) gentle sand the contacts and if preferred renew heatshrink.
I would try replacing the fuseholder and positive terminals (You can buy them separate, if I remember correctly they are Futronics connectors)
can you clarify what you mean by the BMS was bypassed and current path ignored?Wow.
Several issues here...
Looks like the bms was bypassed...
Half the current path ignored, and a scary amount of power was being pulled.
I hope OP responds with photos and explanations of the build before failure...