I think if the working voltage range is higher than the minimum voltage rating of the MPPT, It should be able to produce good power.
MPPTs are only boost circuits in most inverters as they are trying to boost the string voltage to the AC generator input rail. Boost circuits are limited by a maximum input current, thus MPPTs publish a maximum current. The lower the input voltage, the less efficient they are due to higher out to in ratio. That's the nature of DC boost circuits.
The AC generator section converts the high rail voltage to a variable sine wave output. It needs a minimum voltage, usually around 360 volts, to operate. The MPPT boost assures this regardless of string input voltage. But it can operate with higher voltages up to the max input, like 500 volts or so. The problem is that having more voltage than you need increase the in to out voltage ratio and reduces the efficiency. This is the nature of AC generation.
The video above doesn't address these optimizing considerations. Your ideal setup is a string that runs about 360 volts under Vmp conditions at your normal temperature. At this setting, the MPPT has little to no boost requirements and so operates very efficiently (99.9% is sometimes quoted). The AC generator has the minimum voltage it requires and thus operates as efficiently as possible, too. Further, power flowing in or out of the battery is working to/from the 360 volt rail and higher makes that less efficient, too.
No inverter maker I've seen publishes efficiency curves that show the effect of variable MPPT input voltages so these effects are not widely known. A set of charts with the X axis being MPPT input voltage and showing PV to AC, PV to battery, and battery to AC efficiency would be interesting and enlightening.
While it seems many MPPTs have a wide voltage range, it really isn't as wide as it appears once you consider the Vmp versus Voc numbers, and the temperature effects.
The video suggests you can ignore temperature unless you live in a "cold" area, but that's not really true, you should always check temperature to be sure.
There really are three operating points that need to be evaluated for string voltage: maximum, minimum, and ideal.
For maximum, you take the panel Voc and adjust by the coldest temperature you will ever see. Then divide inverter maximum MPPT operational voltage (as opposed to the survival voltage) by the value you computed, round down, that is maximum panels.
For minimum, you take the panel Vmp and adjust by the hottest temperature you will ever see *plus* what you expect the panel temperature rise to be (25 C is a reasonable number, say). Then divide the minimum *full power* MPPT voltage by that number and round up to get the minimum number of panels to produce full power.
For ideal, you take Vmp and adjust by your "typical" temperature. Then divide the MPPT ideal input voltage, usually around 360 volts, by that number. Round to the nearest integer and this is your ideal panel string size. It is usually better to round down more than up which helps with PV to battery and battery to AC efficiency.
You will find string length tolerance is relatively low when you consider all the factors.
An example:
EG4 FlexBOSS21
MPPT max operating: 440 VDC
MPPT min full power: 250 VDC
MPPT ideal: 360 VDC
Aptos DNA-120-BF26-370W
Voc (25 C): 41.4 VDC
Vmp (25 C): 34.5 VDC
Temp co: -0.28%/C
Las Vegas
Min temp: -15 C
Max temp: 50 C
Max voltage is Voc at 25 C (41.4 volts), then adjusted for temperature of -15 C which is 40 C below Voc measurement point. 40 C * 0.28%/C is 11.2% higher. This makes the panel voltage 46.04 volts. Max MPPT operating is 440 volts, so a maximum of 9 panels.
Min voltage to achieve full power is Vmp at 25 C (34.5 volts), then adjusted for temperature of 50 C ambient plus 25 C panel temp rise in sunlight minus 25 C Vmp measurement point. Thus voltage will be 50 * 0.28%/C lower, or 14% lower, yielding a panel voltage of 29.67 volts. To reach the MPPT minimum full power voltage of 250 volts, that takes 8.4 panels, so 9 panels.
Neither computation above is a hard limit as the MPPT survival voltage goes to 600 volts, and being under max power doesn't break anything, but if you want your array to generate full power under all conditions you would see, you need 9 panels.
The ideal MPPT voltage is 360 volts. If we assume 25 C ambient typical conditions and 25 C rise, we will get a panel voltage of 32.1 volts, which works out to 11 panels. If you go with 11 panels, the FB21 will survive that (600 volt MPPT survival rating), but it may stop producing power if the string goes over 440 volts.
The ideal for this setup is probably 10 panels. The chance you go over 440 volts is rather slim (you might not get power in those rare times), and that gets you closer to the 360 volt ideal point n most operating conditions. 11 panels will work too, more optimal in the heat, but you will spend more time above 440 volts and without power.
The basic take away is that string lengths are not as flexible as they appear once you take into consideration all the factors and try to optimize your system performance.
Mike C.