corn18
Village Idiot
- Joined
- Sep 9, 2021
- Messages
- 552
I installed my Lynx distributor today and decided to replace my Blue Sea 250A circuit breaker with a 400A class T fuse. The class T fuse holder is from Blue Sea Systems and the fuse is a LittleFuse 400A class T. Got it all hooked up and tested DC only, Solar and low power AC. All worked great. So I started loading up the inverter. Turned on the fireplace on Lo (800W) and all was good. So I turned on the microwave. 2000W total and all good. So I put the fireplace on Hi. Inverter is outputting 2527W and drawing 286A. Got a low batt alert so I turned everything off. Went to check my wires on the Lynx and HOLY CRAP! The upper nut holding the class T fuse in the fuse holder is glowing RED HOT! Oh crap!
I let it cool off and checked the torque. It was not torqued enough. I must have just hand tightened it when I first installed it. I must have missed it when I checked the torque on every other connection. I tightened it up and redid the test and everything stayed cool.
I'm pretty sure if I had let this keep going, something would have melted or caught fire. And the thing that bugs me is there is no protection for this. This was a piss poor connection heating up but not blowing any fuses or circuit breakers. Scary stuff.
The nut circled in red at the top of the class T fuse is the one that was glowing red hot.