smoothJoey is making sense. The problem is he isn't shouting at you. Rule Number One; Fuses protect wires! I don't know what inverter you have. My 2000W's manual requires 2/0 cable for up to 10 feet.
I only use marine grade cable in van builds, so that is 105C degree. My procedure to select cables and fuses.
#1 Determine the amperes required by the device. (not the surge rating). My 2000W inverter at 12 VDC plus a buffer of 25%. = (2000 / 12) x 1.25 = 208A.
#2 Use the round trip distance from battery to inverter determine the required cable for the needed voltage drop. Using one of the many voltage drop tables on the internet. 4 feet positive and 4 feet negative. Voltage drop chart = 2/0 cable for less than 2% voltage drop.
#3 Use the appropriate ampacity table for your class wire. 2/0 marine single conduit = 330 ampacity. 330A fuse is not available. I pick a 300 amp fuse. Class-T for first catastrophic fuse on LiFePo, MRFB terminal fuses are my choice, or in a pinch, but never for me, ANL.
Note; has anyone noticed the Blue Sea Circuit Wizard seems to give inconsistent results? I used one at GenuineDealz but it is harder to use.