Yes that's what I figured in the drawing but fused or non-fused?
I don't know what is NEC compliant, to run a set of wires to each inverter from the disconnect or a single set to a junction box near the inverters and then break it out to each inverter there?
Also, Would 30A circuit breakers be required after the inverters and before the disconnect?
Obviously line-side tape needs to be fused, I was going to comment on that when I saw the schematic.
You can get fused disconnects of various sizes. I have 30A, 60A, 100A.
This fuse needs to be rated to interrupt utility fault current, typically 22kA or greater (that's what main breakers are rated for.) Many fuses are rated 100kA or 200kA interrupting.
But for a line-side tap, is there an amperage limit? PG&E can put an adapter under the meter, but limited to 40A. Maybe that is just the adapter? But I would think line side tap 60A fuse plus 200A main breaker would be 260A that could potentially be drawn from their wires, not sized for that.
That's why I suggested a 200A fused disconnect between breaker and main panel. Then you can do your own "line side tap" on the line side of main panel, anything up to 200A.
After the line-side tap and fused disconnect, then fuses or breakers for each inverter.
I have a 100A fused disconnect (after a 200A main breaker in meter panel), and I stuffed two, 2-pole 63A DIN breakers in it. Also wired to surge arrestor.
In the drawing, 1/2" EMT? if it is straight, and you can stuff the wires. I like to use oversize conduit.