I installed a Gridboss, Flexboss and two PowerPro batteries on new years eve. No PV yet, running in backup mode. There is a 200A disconnect between grid and Gridboss. Whole house load panel is powered from Backed up Loads output on the Gridboss.

For the first week, all was good. Charged batteries, disconnected grid, house was powered by batteries/inverter. Tested 5 ton HVAC (heat pump) while running water heater. LED lights flickered, but everything worked. Turned the grid back on, and batteries charged. All good.
Something happened, and the house went dark. Flexboss still blinks green "normal" light. No power to the house. I opened the hybrid 1 breaker and put the Gridboss into bypass. That worked. Rebooted system and started looking over the data. I think my emergency heat kicked in, and needed an additional 20kW of power for the heat strips. The Gridboss did not handle this well. It crashed and stayed crashed until I intervened a few hours later. Went back to normal mode, and it happened again. I have better data for that one. See attached graph.

I understand that this would be too much load for the inverter. (I plan to address this by using a smart load to enable/disable the heat strips) But, I thought the Gridboss was supposed to be able to handle up to 200A of pass-through. Why would this load shut things down?
I called support at S2. No solution, but they said they would escalate the ticket. That was two days ago, and I have not heard back.
I have attached some labeled photos. Any suggestions would be greatly appreciated.
UPDATE/TLDR: Surge current to start the 5 ton HVAC was exceeding 200A and tripping the OC protection in the GridBoss. The OCP profile was updated to allow short surges exceeding 200A. This was solved in IAAB-1200 V6 firmware for GB.
I installed a Gridboss, Flexboss and two PowerPro batteries on new years eve. No PV yet, running in backup mode. There is a 200A disconnect between grid and Gridboss. Whole house load panel is powered from Backed up Loads output on the Gridboss.

For the first week, all was good. Charged batteries, disconnected grid, house was powered by batteries/inverter. Tested 5 ton HVAC (heat pump) while running water heater. LED lights flickered, but everything worked. Turned the grid back on, and batteries charged. All good.
Something happened, and the house went dark. Flexboss still blinks green "normal" light. No power to the house. I opened the hybrid 1 breaker and put the Gridboss into bypass. That worked. Rebooted system and started looking over the data. I think my emergency heat kicked in, and needed an additional 20kW of power for the heat strips. The Gridboss did not handle this well. It crashed and stayed crashed until I intervened a few hours later. Went back to normal mode, and it happened again. I have better data for that one. See attached graph.

I understand that this would be too much load for the inverter. (I plan to address this by using a smart load to enable/disable the heat strips) But, I thought the Gridboss was supposed to be able to handle up to 200A of pass-through. Why would this load shut things down?
I called support at S2. No solution, but they said they would escalate the ticket. That was two days ago, and I have not heard back.
I have attached some labeled photos. Any suggestions would be greatly appreciated.
UPDATE/TLDR: Surge current to start the 5 ton HVAC was exceeding 200A and tripping the OC protection in the GridBoss. The OCP profile was updated to allow short surges exceeding 200A. This was solved in IAAB-1200 V6 firmware for GB.