I think the key there is gridboss can pass through "upto 200A"So Gridboss can pass through 200amp. Flexboss can pass through 90a when not using a gridboss. Sounds right.
If there is no grid passing through the Flex (input->output) why does it matter. Should be 200amp always in gridbossI think the key there is gridboss can pass through "upto 200A"
But you'll need multiple flexbosses at 90A each to get there.
With a standalone 18kpv, if running in grid support and your heater calls for an extra 20kW of power, does it seamlessly go into bypass? Seems like some firmware tweaking should allow the same for flex and gridboss comboIf there is no grid passing through the Flex (input->output) why does it matter. Should be 200amp always in gridboss
<EDIT>I can see that I was not clear. The change to the User Manual was for the GRIDBOSS. It can no longer pass through 200A, only 90A. A 55% reduction.
But the second extract is talking about the flexboss not the gridboss?I can see that I was not clear. The change to the User Manual was for the GRIDBOSS. It can no longer pass through 200A, only 90A. A 55% reduction.
OH. You are right. I messed up. I was comparing the wrong two paragraphs. My mistake. I am breathing again.But the second extract is talking about the flexboss not the gridboss?
Sorry, My mistake. You were correct in your assumption.<EDIT>
removed my comment about bait-and-switch.
Looks like current GB manual is 1.1.5 and states 200A. Brucey is correct in the comment below.
OH. You are right. I messed up. I was comparing the wrong two paragraphs. My mistake. I am breathing again.
Can confirm standalone 18kpv will seamlessly pass though grid when needed. Here's a screenshot of my heat pump doing a defrost cycle:With a standalone 18kpv, if running in grid support and your heater calls for an extra 20kW of power, does it seamlessly go into bypass? Seems like some firmware tweaking should allow the same for flex and gridboss combo
But in reading through the GB manual's operating modes, I am no longer sure that "Pass-though" in GB terminology is the same thing as "Pass-through" in 18K terms. I can't find anything in the GB manual that describes a full 200A pass-through to the Backed Up Loads port.
It appears I got this very wrong. I've gone back through the entire thread and studied the GB manual trying to recreate my thought sequence that lead me to this conclusion, and I honestly don't know why I felt the need to write that. On the GB wiring diagram there's clearly a path from the Grid port to the Backup port limited only by 200A breakers. I wasn't drunk, and the post was too late in the morning to have needed more coffee. I had a brain fart and shouldn't have written it down. I'd like to delete that post and go hide under a rock.I don't think EG4 missed this, as it would be the starting point for main Grid connection pass through.
from the spec downloads the GB seems to be rated even higher than the 18Kpv
GB download:
SERVICE ENTRANCE RATED
200 Amp service entrance with a 22 kAIC main breaker, acts as service entrance equipment in conjunction with a utility meter and a 200A Eaton braker (CSR25K).
INTERNAL BUS RATING 350A
INTERNAL FUSE RATING 315A
Can the GB main Grid relays / contactors be seen?
The 18K's exposed accessible units appear to be the models linked below...
I ordered a couple a while back and also a set of 100 amp sets, for (just in case) and "projects".
Also maybe in the settings ? Does the GridBoss also have the input power KW setting as posted by blueforce?
18K :
Max. AC Input Power(kW) (?)
Set [ No Limitation ]
![]()
No biggie, Anyone that posts on forums probably has made a post or two they later thought maybe I got it wrong, Know I have ...It appears I got this very wrong. I've gone back through the entire thread and studied the GB manual trying to recreate my thought sequence that lead me to this conclusion, and I honestly don't know why I felt the need to write that. On the GB wiring diagram there's clearly a path from the Grid port to the Backup port limited only by 200A breakers. I wasn't drunk, and the post was too late in the morning to have needed more coffee. I had a brain fart and shouldn't have written it down. I'd like to delete that post and go hide under a rock.
No biggie, it's a learning experience.It appears I got this very wrong. I've gone back through the entire thread and studied the GB manual trying to recreate my thought sequence that lead me to this conclusion, and I honestly don't know why I felt the need to write that. On the GB wiring diagram there's clearly a path from the Grid port to the Backup port limited only by 200A breakers. I wasn't drunk, and the post was too late in the morning to have needed more coffee. I had a brain fart and shouldn't have written it down. I'd like to delete that post and go hide under a rock.
Given the firmware issues even with the 18kpv now years after release, it much be a nightmare for the firmware guys getting gridboss and flexboss playing nice together. You are truly on the bleeding edge.The GridBoss tripped just before 1am this morning. This time it threw some error codes. When I reset the system by cycling grid power to the GridBoss, I also turned the breaker off to 1/2 of the heat strips, so that I could hopefully get some sleep.
I turned the 2nd heat strip breaker back on when I got up at 6:30. At about 6:45, EM heat was running with no issue. When I turned it off, the GridBoss tripped again. I don't think the problem is solved. I am running Gridboss Firmware version IAAB-1200 and FlexBoss version FAAB-1E1E.
View attachment 271715
View attachment 271718
I use the breaker to "enable" the heat strip banks. When I turned off EM heat this morning, I did that with the HVAC thermostat. As soon as I clicked it, the lights went out.Looks like the heat strips run for a while and then gradually draw more current until something shorts out? Just guessing here, it's clearly something very far out of the ordinary. Do you have a clamp ammeter you can measure the individual heat strips with to see if there's any significant difference or change over time?
Edit: When you turned the heat strips _OFF_ the GridBoss tripped out on overcurrent? Was it just the second heat strip breaker?
Are you using the breakers to enable/disable your heat strips? _Shouldn't_ be a problem, but not sure they are rated for a lot of cycles.
Did GB log the error codes?
I'm guessing this common use case wasn't tested during gridboss development. Waiting for the heat pump to be blamed for being "noisy".Yeah, check the event log for things that happened in the first trip just before 1AM, that's either a smoking gun or a red herring. 8*)
Load dumping from turning off the heat strips might send some power back to the grid, but shouldn't throw an overcurrent fault.