grounding electrode location

User has a panel array, power house, and house all in a straight line.

panel_array---50'---power_house---80'---house

The plan is to have the n-g bond in the power house and the grounding electrode will also be in the power house.

Is the voltage gradient over 80' between power house and house an issue?

@FilterGuy
@NorthTown2022
A separate structure is required to have a grounding electrode. One is needed at the power house and one at the house.

The house will not have N-G bond, the power house will have N-G bond.
 
Sorry I wasn't clear. I'm talking about the voltage gradient between the house electrical system and the earth it sits on.
The house electrical system will be referenced to the earth at the grounding electrode 80' away from the house.


There could be a voltage gradient between earth at the house and the earth at the grounding electrode.
Won't be a gradient as NEC requires a EGC be run to house grounding busbar and the grounding electrode at the house.

If you don't follow the "rules", then yes, you will have a voltage gradient.
 
@John Frum is referring to my installation.

With multiple out buildings I am understanding that figure 3 'best' option will be most suitable in my situation. Is there a rule to dictate the gauge of copper conductor used to daisy chain grounding electrodes? Also I suppose the copper conductor should be insulated?
In my state, #6 bare copper in the trench.
 