Grounding on Off-Grid PIP – 1012LV-MS ??

sloweb

New Member
Joined
Mar 21, 2022
Messages
1
I am setting up a 1012LV-MS that will only be off-grid. Maybe connect a generator to charge battery in the future. I don't see a chassis (or other) grounding lug to connect to grounding rod. I gather that the ground/neutral is bonded in the unit. So I am guessing that I should treat it like a generator - use no external grounding. Is that the correct way - no ground rod? Or should I use the ground lug of the AC-In connection and take it to a ground rod?
Thanks...
 

Zil

Just another ass on the web
Joined
May 27, 2020
Messages
1,833
No earth ground needed in such a system. The earth ground (green) is referenced to the inverter or the generator.
If you connect to the grid the green earth ground must connect to the main entry panel ground.
 

Shimmy

Solar Enthusiast
Joined
Feb 22, 2022
Messages
239
You should always have a ground rod connection; the question is really where you attach it.
 

Zil

Just another ass on the web
Joined
May 27, 2020
Messages
1,833
No! sometimes you do not have a ground rod. Only when connected to the grid is there a ground rod.
 

Shimmy

Solar Enthusiast
Joined
Feb 22, 2022
Messages
239
No! sometimes you do not have a ground rod. Only when connected to the grid is there a ground rod.
With US codes?! What section of the NEC are you referencing? The only exemptions I see are for portable systems.
 

Zil

Just another ass on the web
Joined
May 27, 2020
Messages
1,833
Exactly what we are talking about.
"......1012LV-MS that will only be off-grid. "
 

Shimmy

Solar Enthusiast
Joined
Feb 22, 2022
Messages
239
Exactly what we are talking about.
"......1012LV-MS that will only be off-grid. "
There are exceptions for portable and vehicle mounted systems where bonded to the vehicle, but not for off-grid systems.
 