Is it necessary to drive a long copper grounding rod into the ground and connect it to a small system? For instance, a 24v MPPT, connected to max 1500w 110v 20a in the panel array.
Why grounding is necessary in power system?
One of the most important reasons for grounding electrical currents is that it protects your appliances, your home and everyone in it from surges in electricity. ... If your electrical system is grounded, all of that excess electricity will go into the earth — rather than frying everything connected to your system.
Rubber I san insulator it cannot conduct any electricity.So it seems grounding is being accomplished through the 4 tires.
If you have a physical "PumpHouse" which has a Steel Well head in or near it, a Well Casing is allowed to be used as a Ground in many Jurisdictions. Check with your codes.The design will be the 3 systems staged in a sort of a "pumphouse" built just for them, so the panels can be placed in good sun but close proximity.
Actually, no.I believe in some jurisdictions, the code requirement is two 8' grounding rods, connected SERIALLY to each other. My understanding of the grounding code is that there may be multiple below-ground grounding points, and multiple above-ground attachment points, but all the above-ground points are connected to the below-ground points at one single junction only. If you do not do this, the grounding system becomes a lightning attractor! Let's say you pound a rod along side the foundation of the building on the right side of the house. You could then pound a second rod 10' out from the foundation, still on the right side, and connect the two rods via a solid copper wire. Your above ground grounding wire gets attached to the nearest ground rod only.
What you must NOT do is drive one rod on the right side of the building, and another rod on the left side of the building, connecting the two rods at two different places along the above-ground grounding wire.
Could I get more detail on the minimum spacing for dual ground rods? I have two rods spaced 3 feet apart (due to only three feet penetration depth). What is the reasoning on the separation - and lightning attraction. These are equipment ground rods for a 3kw panel array.Actually, no.
The grounds MUST be connected to an unbroken grounding conductor. The water pipe, and BOTH ground rods spaced at LEAST 6 feet apart, must be connected to a single unbroken grounding conductor.
Array ground is different.Could I get more detail on the minimum spacing for dual ground rods? I have two rods spaced 3 feet apart (due to only three feet penetration depth). What is the reasoning on the separation - and lightning attraction. These are equipment ground rods for a 3kw panel array.
Sometimes I have dug down to the wet soil level and laid ground rods horizontally in a trench .. forgive me.Array ground is different.
The twin ground rods spaced minimum of 6' apart is for breaker panel grounding
Yup, this is an acceptable alternative... as is driving the rods at a sharp angle when bedrock is encountered...Sometimes I have dug down to the wet soil level and laid ground rods horizontally in a trench .. forgive me.
What is the definition of "an unbroken grounding conductor"?Actually, no.
The grounds MUST be connected to an unbroken grounding conductor. The water pipe, and BOTH ground rods spaced at LEAST 6 feet apart, must be connected to a single unbroken grounding conductor.