Please post a picture of the breaker.That is not how breakers work.
Does the breaker have a visual indicator that it has tripped?
Please post a picture of the breaker.That is not how breakers work.
Please post a picture of the breaker.
Does the breaker have a visual indicator that it has tripped?
I manually turned it off. Now thinking about it more, the breaker couldn’t be tripping because the battery stays on overnight as the soc and run indicator lights remain on even when the PV input icon turns off on the inverter and isn’t receiving voltage.That breaker has a visual trip indication.
Did it trip or did you manual turn it off?
Cool, we are making progress.I manually turned it off. Now thinking about it more, the breaker couldn’t be tripping because the battery stays on overnight as the soc and run indicator lights remain on even when the PV input icon turns off on the inverter and isn’t receiving voltage.
Yeah. My panels are not idealMy not be the problem but 325 watt panels usually have a VOC of around 50 volts. I think your mppt is 145 volts. 50x3=150 volts
Will do, buddy. Appreciate it!I suggest that you turn the system back on.
Assuming it is in the failed state tomorrow morning use your dvom to check the voltage on the all_in_one at the pv terminals and at the system side terminals.
Also take a picture of the all_in_one and battery lcd screens.
Report back and lets see if can get another 10 yards down the field.
My inverter specs show max vdc input 145 and the panel VOC is 45.5v. Probably a bit too close. I’ve tested the array voltage and they haven’t tested over 120v at any point however.My not be the problem but 325 watt panels usually have a VOC of around 50 volts. I think your mppt is 145 volts. 50x3=150 volts
I suggest that you turn the system back on.
Assuming it is in the failed state tomorrow morning use your dvom to check the voltage on the all_in_one at the pv terminals and at the system side terminals.
Also take a picture of the all_in_one and battery lcd screens.
Report back and lets see if can get another 10 yards down the field.
So the sun has completely went down here and the tiny bit I thought I knew is perhaps backwards.
Now the breaker is in the up position but the indicator is green. I flipped the breaker to the down position it turns green. Back up, red again.
I reset the inverter and the breaker (remained red) but the Inverter screen shows panels connected. The battery indicator on the inverter screen is solid.
When the sun went down the breaker was up, but red. The inverter screen showed no panel connection but the inverter battery symbol was blinking like it was charging.
I’m totally confused and apologize for being such a noob.
What do the red and green status indicators signify?Breaker currently in up position with red indicator but battery indicator lights are on and I’m getting power from it
Bulk is currently 56.4 and float 54.0. Do you think I should adjust one or the other?What are the charger bulk and float voltage settings at? Float should be about 0.5V less than bulk. It will not start charging again until the float voltage level is reached.