You did not specify which Growatt 3000 watt model you have, but one spec I looked up says PV input low limit of 120 vdc.PV terminals at Inverter reading between 60-100v and ranging very fast.
Yes, move float up to 56.0V. At 54.0V for float, it will not resume charging until you get down to 3.375V per cell.Bulk is currently 56.4 and float 54.0. Do you think I should adjust one or the other?
I'm having the same problem in the morning, did you find a solution?Hi having the same problem , i have growatt 5000es , 8 panels in series Canadian 595W each , at night the battery reaches the cut-off setting in the program of the inverter . This is normal the inverter should cut the loads and turn off , and when sunrise it should turn on and start charging the battery and bring ac to loads normally ( i have another inverter in my parents home usually like this ) but my inverter does not start up by morning till i turn the inverter off then on by the switch of the inverter . Any body have new update for fix for this problem ?
I talked to Growatt, they said they will send me a firmware update, but they weren't clear if that will solve the problem.Write an email to Growatt Service and see if they have a firmware update that addresses the problem.
Unless you have float setting 0.5V below bulk setting, the unit will not begin charging until the float voltage setting is reached on discharge. You have to use USE and set the voltage levels for bulk and float.Same issue with my Growatt 3000 stacked 2 together in parallel. Morning charging does not occur unless I disconnect battery power and restart both inverters, then it charges normally. I have let the system go all day and it never charges until I disconnect power and restart.
Hello everybody. Same exact problem is happening in different sites we have instaed Growatt SPF 5000ES at. This problem starts to happen several months after installation. I believe it's an internal component issue not a setting (no one changed) or firmware (it was working normally).Hi the unit is reaching cut off level which is 44V at night and the System shuts-down ( till now its ok ) but at morning at 8:00 Am when the full sun is reaching the 8 pannels, the inverter should start On and start charging ( batteries are 44V) and give AC to loads, the inverter does not load till i turn it off then on . ( after that all is ok)
HF AIO inverters needs the full inverter running to charge battery from HV DC bus. So bottom-line is battery has to have enough capacity left to supply inverter idle power plus SCC driver overhead power.Hi the unit is reaching cut off level which is 44V at night and the System shuts-down ( till now its ok ) but at morning at 8:00 Am when the full sun is reaching the 8 pannels, the inverter should start On and start charging ( batteries are 44V) and give AC to loads, the inverter does not load till i turn it off then on . ( after that all is ok)
Hi the unit is reaching cut off level which is 44V at night and the System shuts-down ( till now its ok ) but at morning at 8:00 Am when the full sun is reaching the 8 pannels, the inverter should start On and start charging ( batteries are 44V) and give AC to loads, the inverter does not load till i turn it off then on . ( after that all is ok)
I've just encountered this for 3 days after a couple of weeks of running/auto-starting PV charging. I'm still waiting for a warmer night to see if it's something related to battery BMS shutting off at night during freeze or it's a Growatt internal component failing like @hazim mentioned. Have you guys found issue/solution yet?Hello everybody. Same exact problem is happening in different sites we have instaed Growatt SPF 5000ES at. This problem starts to happen several months after installation. I believe it's an internal component issue not a setting (no one changed) or firmware (it was working normally).