Not individual positive and negative.I thought the battery cables needed to be the same length when you use 2 inverters , something about current sharing, I will read the annual again but it says something about keeping all battery cables the same length
Total length per inverter, needs to be the same.
The reason is that each inverter needs to see the same voltage, when stacked as a single system. Conductors have resistance. Longer Conductors have higher resistance. Resistance creates voltage drop.
So for both inverters to see the same voltage. The total length (positive and negative added together) for each inverter needs to be the same as the other inverter/s.
For example: inverter #1 could have a positive cable of 6ft and a negative cable of 3ft.
Inverter #2 could have a positive cable of 3ft and a negative cable of 6ft.
The resistance would be the same. Because the total length (round trip) is 9ft, for each inverter. Therefore both inverters would see the same voltage.